Just working from the numbers given. 150vDc max for the controller should allow for a 120v input with 20% margin even with cold weather.That would still blow up.
Just working from the numbers given. 150vDc max for the controller should allow for a 120v input with 20% margin even with cold weather.That would still blow up.
Since he blew up the second MPPT, can we assume he did not order a third?Your charge controller can only accept 1040W. With ten 200W panels, you have double the rated power input that your charge controller can handle. You have too many panels.
You are able to put 3 in series and still be under the 150V. Your panels are 24V nominal, but have a VOC of somewhere near 40V (assuming they deliver 5.2A as you stated).
In order to get the most power into the charge controller, I would recommend 5 in parallel. That allows the max power and you're still within the voltage and current ratings of your charge controller.
I did not see Brad suggest any connection, other than him suggesting you should stop blowing stuff up.Mr.thisisme… What do you think of BradCagle connection?
5 in parallelNow that everyone has the specs of my charge controller and the panels. Do me a tremendous favor. Tell me exactly, in order to maximize as many panels as possible, how to connect them so I do not blow up my charge controller. And I will do it without fail.
First thing, is you have to measure voltage before you connect anything again. Pretty sure there is a rule here if you blow up three CCs people are forced not to help you anymore.Now that everyone has the specs of my charge controller and the panels. Do me a tremendous favor. Tell me exactly, in order to maximize as many panels as possible, how to connect them so I do not blow up my charge controller. And I will do it without fail.
What is the lowest temperature on record for your area ?Now that everyone has the specs of my charge controller and the panels. Do me a tremendous favor. Tell me exactly, in order to maximize as many panels as possible, how to connect them so I do not blow up my charge controller. And I will do it without fail.
It doesn't matter. OP needs 5 in parallel. The voltage will stay well within the limits.What is the lowest temperature on record for your area ?
That is needed to calculate how much each panel will go above the specified Voc of 45.4 Volt
Depending on lowest tempYou can do 3 in series
I would say put 1.2 to 1.25 times max power of CC on the input:Given you have 10, you should do 2 in series
If OP uses 5 in parallel, there will be 1kW of power and still be within the voltage and current specs of the charge controller.You can do 3 in series
Given you have 10, you should do 2 in series
If OP uses 5 in parallel, there will be 1kW of power and still be within the voltage and current specs of the charge controller.
Yes, or get one larger charge controllerHere in Southern Ohio, extreme temp, 3 below Fahrenheit
I will do 5 in parallel.
One last question. I have a total of 10 panels I would like to utilize. So my best option would be to have two sets of 5 panels in parallel connecting to their own charge controllers.
Is this correct?
What are you trying to charge?Here in Southern Ohio, extreme temp, 3 below Fahrenheit
I will do 5 in parallel.
One last question. I have a total of 10 panels I would like to utilize. So my best option would be to have two sets of 5 panels in parallel connecting to their own charge controllers.
Is this correct?
The specsheet of the manufacturer does not say the Voc temp coefficient on their website, which is a pityHere in Southern Ohio, extreme temp, 3 below Fahrenheit
Like I wrote before:One last question. I have a total of 10 panels I would like to utilize. So my best option would be to have two sets of 5 panels in parallel connecting to their own charge controllers.
I built a tiny house so… Everything within reason.What are you trying to charge?