There is outside flex going to exterior battery disconnect.
I wasn't sure that I would be allowed an indoor battery by the AHLJ and I still need to secure this to the wall. On my list today:Is battery cart secured against seismic events?
The automatic transfer switch is fed by a 50 amp breaker (6/3 romex and a utility disconnect in between). So the sub panel has 60 amps from utility, 25 amps from battery inverter, and 42 amps from PV (during the day). So the load panel can handle between 75 amps and 117 amps.Your schematic has a backup loads panel, but no provision to supply main panel.
Yes, the combiner box has a PV RSD and back feed breaker 50 amps has been tied down.PV RSD maybe breakers inside that box.
No, not as far as I know. The meter needs to tell where the RSD is located.I thought maybe RSD was also supposed to be within 10' of meter.
There is a small bit of NM liquid tight and I need that flexibility. Perhaps, I can change that to metal liquid tight at next update.plastic flex
IMO battery disconnect is also ABS as are the two white junction boxes (yet to paint them) at the top.Zooming in, the boxes are metal.
All the PV circuits are AC and terminate into combiner box. Please see the SLD in the first picture.Are the PV circuits all AC?
I did that just to impress the inspector. Some of those are totally superfluous. Have to remove them and clean with acetone (after killing the energy!).overkill of stickers
Yes. Liquid tight and non metallic. As is the BOX that came with the disconnect.exterior battery disconnect.
This is a point of worry for me (right now I manually shut down strings). Currently, I don't have PTO and so I have to test off grid. In the off grid mode, during the day, once we fired up the steam room (7.5KW) and it took that in complete stride. The charging turned into 1.1 kw discharge. However, once in the evening, I accidentally turned on steamer while in off grid mode. At that time, the max energy capacity was 6kw and the SMA system shut down due to overload and came back on by itself, still in off grid, after 2 minutes (fortunately, steamer was off by then).Microinverters are UL-1741-SA, so they may work fine with SBS frequency shift when grid is down. But no guarantees. People are having mixed results with other microinverters and other high-frequency battery inverters.
MORE UPDATE:Folks:
After a few revision because after the permit, store ran out of stock on modules, I had a success. Today, I also got my city to approve the installation after the inspection.
I am attaching the SLD and the pictures in the spirit of show and tell.
View attachment 144741View attachment 144745View attachment 144744View attachment 144743
Thanks for all the support and I hope to continue to learn from you all.
Anil
What kind of deal did you get on those?I see you have Sunny Boy Storage with BYD.
I picked up 3x SBS 5.0, and just bought 2x LG RESU-10H. Can't tell if they are -C (SMA) or -R (Fronius)
The serial number I checked is subject to recall, so my plan is to exchange for new ones.
Mighty expensive lock for a breaker lock out..Can be done with individual breakers too.
Switches only used for some things.
In our training, "line of sight" isn't good enough, except for an unplugged cord. (and there are hasps for cords, too.)
What kind of deal did you get on those?
That’s why I askedAbout $1900 including shipping for 3x Sunny Boy Storage 5kW (plus sales tax.)
$3000 for 2x RESU10H, local pickup (plus sales tax.)
You know I don't buy such stuff without a deal!
Keep an eye on the early bird adoption incentives for NEM3. You get some more favorable sell-back rates. Probably if your NEM1 expires 1 year after early bird goes away, maybe you will be ahead if switch 1 year early. Probably almost a wash (but I haven't done the math carefully)For my NEM 1.0, may keep my head down unless they bump me on to NEM 3.0. Then, adding SBS would be an excuse to double export wattage (battery inverter allowed to be more than PV inverter.)
I'm not sure what's what in terms of ESS UL listing. Because RESU-10H is 3x 48V packs in series and bidirectional boost converter, it ought to be listed on its own. The inverter doesn't directly interact with batteries (unlike the stackable HV BYD.) But they may not have obtained listing to some new UL xxxx.