Hi,
I've recently installed a Voltronic VMIII 5kw Inverter with an Yilink battery 7.2kw LifePo4.
Battery Mode: LIB
There is one cell unbalanced, so the battery cannot reach the full charge voltage of 52.5V (it stays at 51.6/51.8) and the BMS trigger an OVP (at 3.7V)
After that, inverter stop the charging for a few seconds but then it's enabled again generating a loop.
In the battery display I can see lot of OVP alarms because of this.
If I set Battery Mode: USER with same BULK/FLOAT voltages the loop doesn't occur: In this way charging it's disabled until the over-voltaged cell goes down at 3.4V (as configured in BMS (Cell OVP Release using PBMSTools software)
Why are there these problems when setting up a communication protocol? shouldn't it be more secure than USER mode?