I can't tell from the manual.
Often times you just need to short 2 pins to turn the unit on.
Perhaps this CR-8 manual can help. it does show the RJ-11 wiring diagram
This is not the same inverter as it is the CP version, but in the manual it does describe the RJ-11 wiring on page 31
3-2-1. Remote Port (RJ-11) The SP Series Inverter can be compatible with CR-8, and CR-16 remote control via RS-232 Communication. Before using the remote control, make sure the main switch on inverter must be at “ REMOTE” position.
Pin Number Signal Description ①
1 Reserved --
2 GND The same polarity as the battery negative side
3 RXD RS232 RXD
4 TXD RS232 TXD
5 RMT Remote controller panel (positive)
6 VCC Internal power for remote controller
Table 28. SP Series Remote Port : RJ-11 3-2-2. Remote Control Green Terminal Remote control green terminal ② may be connected to a Form C relay for “FAULT” indication. When “FAULT” occurs, the relay switches.
Figure 13. Remote control terminal Item Description Item Description
1 Dry contact (Normal Open)
4 Enable+ (ENB)
2 Common
5 Enable- (ENB)
3 Dry contact (Normal Closed)
6 Ground Table
29. Dry contact terminal definition Note! Pin-6 is the same polarity with battery negative electrode.
32 Note! Fault conditions include Input under / over voltage, output short circuit / over load, over / under temperature.
Caution! Please follow the following steps for the installation Before installing the inverter, make sure the main switch is at “OFF” position. Before using the remote function, make sure the main switch pressed toward “REMOTE”
Use 20 ~ 24 #AWG wire to connect the remote control terminals Figure 14. Wiring for control