Wouldn't I be able to do the same with the Radian?
Yup, no problem.. you could do the same with any battery inverter you want when the grid goes down.
The important part is to install a "generator interlock" so it is
not possible to have the utility grid and battery inverter or generator connected to your home at the same time.
Installing a generator breaker also allows you to.. wait for it (LOL).. legally backfeed a regular generator into your home!
Its a nice feature to have.
I also installed a patch circuit from a generator plug (gen inlet tap) outside my home, to a receptacle near my breaker box. There is nothing connected to it.. its just an inlet plug outside for the generator to hook up to and a receptacle inside for me to plug into.
I then use 4 wire SO cords (with appropriate plugs) to configure the system however I want.
This patch circuit allows me to configure my home's power multiple ways:
1) Utility grid powering home with grid-tied solar (Normal mode of operation)
2) Off grid battery system powering home with solar support. (Normal mode when grid goes down)
3) Off grid battery system powering home with solar support and generator support for when we get a long string of cloudy days.
4) Generator powering home on its own. (no solar or battery support)
The really nice thing about being able to charge batteries with the generator is that generators spend most of their time wasting energy and only putting out 10% to 30% of their ratings. Generators run best at around 80% of what they're designed for.
Since I can set my inverters to draw a specific amount of energy from my 6kW generator, I tell it to draw 20 amps, which works out to about 4800 watts. When my battery is low and there's no sunshine for solar, I can turn on the generator and the battery inverter will load it down to almost exactly 20 amps. Regardless of what the loads in the house are doing, the generator will run smoothly at a 20 amp continuous rate.. this reduces wear and tear on the generator and maximizes its efficiency.
The other thing this does is to limit the generator run time. 4800 watts into my 25kWh battery bank means I can run the generator for about 5 hours and the battery will have enough juice to last for another day.. hopefully the sun comes out by then, but if not, I just run the generator for another 5 hours. Much better than it running all day wasting energy and wearing itself out.