42OhmsPA
What's in a title?
Check prices at wirenco, they were cheaper than Nassau, after shipping, when I ordered.So I can get 2-2-2-4 for $1.59 a foot and then 1-1-1-3 for $2.09, might as well go with the larger to be easily within 100A rating?
1-1-1-3 ALUMINUM SER CABLE
Specifications : Insulated Cond(s) Size AWG : 1, Bare Conductor Size AWG : 3, Nominal O.D. Inches : 0.973, Approx. Weight lb/1000FT : 435 lbs, Ampacity at 90°C : 115 Amps, Ampacity in dwelling : 110 Amps. Standards : Ampacities based on National Electric Code, 2005 edition, section 310-15, 90°C...nassaunationalcable.com
2-2-2 Aluminum SER Cable with # 4 Ground Wire Cut to Order
Applications:SER is type SE, Style R cable, used as an above ground service entrance cable, a panel feeder and in branch circuits. The cable is rated at 600 volts and 90°C for use in wet and dry locations. SER cables are LEAD FREE and RoHS compliant.Construction:Insulation - Color coded...
shopwirenco.com
Zanydroid covered it.Thanks. So do I use something like this for the feed from the main panel? Or does the 1-1-1-3 connect directly to the sub panel, and just have a 100A breaker at the main panel?
Square D QO 100 Amp 22k AIR QOM1 Frame Size Main Breaker for QO or Homeline 125 or 100 Amp Load Centers QOM100VHCP - The Home Depot
Protect a breaker panel in a load center with this Square D by Schneider Electric QOM1 frame size 100 Amp Double-Pole Main Breaker. Used for overload and short-circuit protection of your electrical system,www.homedepot.com
I chose this option.You can use main lug (no breaker) and rely on the breaker at the main and feeding from the Rosie to protect the wire.
Both items I linked above in the attached photo.
I'm looking forward to Rosie reports.