when i made the decision to pass over the 'parallel operation' section of these manuals i remember thinking 'haha prob gonna miss something THERE'
and indeed, i see the recommendation. on the 3048 3kw claims a max line mode charge rate of 60A. It asks for 100A breaker on the battery here (mentioning a 83A max current on p.7) and 48A on the AC input. I checked the 5048 as well and found p much identical details for the ratings.
That sounds right, more or less, for protecting at max combined line mode load and max battery charge current. I guess what tripped me up was the call for 10AWG wire on that AC input line. I would rate 5.7kw @ 120VAC/50A at 4awg/6awg for any length to about 15 feet, as an input from gensets or EV charge station/ shore power connection.
when i made the decision to pass over the 'parallel operation' section of these manuals i remember thinking 'haha prob gonna miss something THERE'
and indeed, i see the recommendation. on the 3048 3kw claims a max line mode charge rate of 60A. It asks for 100A breaker on the battery here (mentioning a 83A max current on p.7) and 48A on the AC input. I checked the 5048 as well and found p much identical details for the ratings.
That sounds right, more or less, for protecting at max combined line mode load and max battery charge current. I guess what tripped me up was the call for 10AWG wire on that AC input line. I would rate 5.7kw @ 120VAC/50A at 4awg/6awg for any length to about 15 feet, as an input from gensets or EV charge station/ shore power connection.