MPP Solar 5048 input voltage

Oneofhis

New Member
Joined
Aug 26, 2020
Messages
12
Hello All, I am just getting started so I have the first question. The 5048 Charge controller/inverter has a limit of 145 VOC input to either of the two controllers. I would like to attach 6 X 400 watt panels in a 3S 2P , which would give 149.9 VOC at the solar panel output. The manufacturer says no way, 2 panels in series max. So my question is there a way to adjust the voltage down a bit before going into the MPP Solar 5048?
 
No. Go 2S3P. You also want to allow for voltage spikes due to cold weather.
 
No. Go 2S3P. You also want to allow for voltage spikes due to cold weather.
The MPP 5048 only has 2 solar inputs, so 3 in P wouldn't work would it? I was thinking of attaching a voltage regulator, have no idea if that would work or harm the panels in any way. Looks like I'll need one extra charge controller for the 3rd P leg. Thanks!
 
Why won't it work? You'll only be using one of the inputs. You will have a single 2S3P array that is connected to one of the charge controllers.
 