Just coming back to the high surge demand for this pump, would a set of super-capacitors in parallel with the inverter be a solution? The super-caps dump the momentary 160A required at startup leaving the inverter then to power the running current?
Sure thing. Looking back on April, I raised my cut-off to 22.9 from 22.6. That did work. That is, it was able to disconnect the loads yet still able to charge the bank because it averted a BMS cut-off. That would be specific to your batteries, which are Lion Energy LPE in my bank.I am running a similar system can you post your settings screen.
Thanks in advanced!
No need to reinvent the wheel. Pump manufacturers already market startup control boxes with start capacitors the size of your fist.Just coming back to the high surge demand for this pump, would a set of super-capacitors in parallel with the inverter be a solution? The super-caps dump the momentary 160A required at startup leaving the inverter then to power the running current?
Anything look crazy?
01 - Output source priority SbU
0205 - Solar supply priority bLU
10 - Charger source priority CSO
17 - Bulk charge 28
18 - Float charge 27.5
19 - Low voltage cutoff 24
20 - Bat. stop disc charge when util avail 24.5
21 - Bat. stop charge when util avail 26
I'll set it (18) down a bit then! Thanks for the reply! Can I ask what "re-bulk" is all about?
Be careful with 10 CSO. I've seen that setting allow the batteries to drain below the low voltage cutoff. If it sees any PV at all it won't charge from the grid. What happened was as the sun was going down I was only getting 50 or so watts from each array. At the same time my batteries were drawing down under load I was really surprised to see the inverters allow the batteries to draw down past the low voltage disconnect voltage settings. I use SNU and allow the inverters to manage between the grid and solar. Initially it bugged me because it looked like it was drawing from the grid all the time even when I had plenty of solar available. That's not really the case. The LCD looks as though the grid is engaged but it's really just a function of the software. It flips between the grid and solar as necessary and from inverter to inverter as necessaryJust starting up our two LV2424 in parallel, L1 and L2 at 120v/60Hz setup, LiFePO4 - 200 Ahr. We are playing with settings now!
Just had the "dead at wake-up" this morning and looking to fine tune...
Here is where I am at present, I think I hit hit BMS low voltage cutoff MPP was at 23v and have set it to 24v.
Anything look crazy?
01 - Output source priority SbU
0205 - Solar supply priority bLU
10 - Charger source priority CSO
17 - Bulk charge 28
18 - Float charge 27.5
19 - Low voltage cutoff 24
20 - Bat. stop disc charge when util avail 24.5
21 - Bat. stop charge when util avail 26
I have only ever had it set toReally appreciate all the info you are all sharing! I'm in on the (10) snu setting...
I've only been up and running a few weeks so far and just noticed the last couple days when playing with settings that setting 01 - Output source priority (solar supplies first), when set to SbU, my lights are flickering and it stops when I switch back to SUb. I only have a multi meter and the LCD on the LV2424's but I think maybe the AC output frequency might be fluctuating when set on SbU. Any thoughts on this?
Same here
Yes, mine don't flicker on that setting either. I guess there is no reason to set it to SBU...
Thanks! That's awesome. I put it in the wiki here.I got so confused a while ago (not that it's improved a lot) I charted the settings from the manual to the "solar power" pc software screens, put the manual / LCD numbers in (##) and matched them to the pc software screen, inverted colors so I could print it on B/W printer... Of course, my settings are not important... May help others?
View attachment 27105
just studying this thread. My chart for LiFePO4 SOC vs various Voltages show 24.0 volts = SOC of 9.50% ... on LiFePO4 setups, but see somebody mentioning Gel Cell in post above.I'm struggling to understand why you would want to set a low voltage cut-off above 24V. A battery voltage of 24V would indicate a state of charge of around 50-60%, why would you want your inverter to cut-off above this?