Okay makes sense. For the grounding cable, i tried putting a #6 bare copper wire through conduit and it was pain the neck. Does it have to be #6 bare copper OR can I connect a #10 stranded wire for this system size which is easier to push through conduit?No matter what you'd have to run a ground line back from the array to the other ground rod. You can't have two independent ground rods in your system. On top of that it is no longer recommended to have separate ground rod by your array. Just run another cable from the array for ground that connects with the ground for the rest of your system. So from your array you will have PV positive cable, PV negative cable, and a grounding cable.
If it it is protected by an enclosure, or conduit, 10AWG stranded should suffice.Okay makes sense. For the grounding cable, i tried putting a #6 bare copper wire through conduit and it was pain the neck. Does it have to be #6 bare copper OR can I connect a #10 stranded wire for this system size which is easier to push through conduit?
I am using two #10 stranded (red & black) PV wires. So then is it okay to use just one more #10 green stranded wire which connects panels & inverter to one grounding rod?Of particular interest to PV installers is Section 250-122(b) of the NEC. It states that if the current-carrying conductors have been oversized to minimize voltage drop, then the equipment grounding conductors must also be oversized in the same proportion. But the grounding conductors never have to be larger than the current-carrying conductors. Oversized conductors (above minimum ampacity requirements) are frequently used on long circuits between the PV array and the charge controller to reduce voltage drops in these lines. Table 8 in Chapter 9 of the NEC shows the cross sectional area of different sized conductors, and the calculation is straightforward.
What size (awg gauge) cable are you using for positive and negative from the PV Array (the current carrying conductors)
The grounding conductor from the PV panels would tie into the ground bus in your breaker panel.I am using two #10 stranded (red & black) PV wires. So then is it okay to use just one more #10 green stranded wire which connects panels & inverter to one grounding rod?
placed the two ground rods 6 feet apart and as @wdwtx2.0 states, #6 bare copper connected to the panel ground bar on one end and to the 2 ground rods. having no splice in the #6 copper going to the ground rods.
Then run a ground wire with the current carrying conductors from your PV array and ground that at the inverter.
Run a ground wire from your battery to the inverter.
Run a ground wire from the inverter to the ground bar in the electrical panel.
Edit: as a general rule, always run a ground wire with your current carrying conductors. From where the current carrying conductors originate from and to the equipment they terminate at.
yea but you want to bring the grounding straight to the grounding in the breaker, not through the inverter firstI am using two #10 stranded (red & black) PV wires. So then is it okay to use just one more #10 green stranded wire which connects panels & inverter to one grounding rod?
With this configuration,watch
watch 14:00 - 14:25 that is what your diagram shows, which is dangerous
You want to run a wire from the panels back to your main grounding area to go into that ground rod and only that ground rod
at 14:34 you can see what to do
View attachment 217107
yea but you want to bring the grounding straight to the grounding in the breaker, not through the inverter first
With this configuration,
1. I still have to connect inverter ground to sub panel ground, correct?
2. Do I need to do Neutral-GND bond at the sub panel?
# 1 - ok#1 - yes - all panels, boxes shells, PV frames, etc connect to a single grounding connection and that is connected to a single ground rod.
#2 - no - only have the neutral ground bond in your main panel. Make sure your inverter doesn't switch a N/G bond in unless it has a transfer switch and completly disconnects all wires including the neutral. There is generally a settin if this is possible and you want it off
# 1 - ok
# 2- Inverter will be connected to a sub-panel with no AC input from main panel. Completely off-grid. In that case, since there is no Neutral-GND bond at inverter or sub-panel, is preference to do it in sub-panel or at inverter?