According to what I've read here, https://diysolarforum.com/resources...nes-for-solar-panels.143/version/324/download
the NEC does not accommodate highly "over-panelled" solar installations.
I live in a very solar-adverse location. If I did not fear the high likelihood of losing commercial electrical power for a lengthy or indefinite period of time, I would not even consider solar power as anything more than a hobby and curiosity. Since before the last winter solstice, I have been taking output measurements of portable Ecoflow 220W bi-facial panels as well as a pallet of SunPower E-Series: E20-330-COM-MLSD panels. It would behoove me to install the SunPower PVs in two highly over-paneled 2s9p arrays on the roof of my shop to feed my two Ecoflow Delta Pros.
If I were to install small 2s2p arrays, no OCP devices would be required by the NEC, because the arrays would contain only two strings each. On the other hand, a small array isn't really worth installing where I live but 2s9p arrays could support food refrigeration and a well pump but the NEC says they require very large fusing and wire sizes.
The NEC requirements don't make sense to me in the over-paneled 2s9p system, because the worst case currents used in the NEC calculations will never occur with the 2s9p array feeding an Ecoflow Delta Pro SCC (15A / 150V max. solar input) unless there is a fault somewhere and then I would happily welcome under-NEC-spec fuses to blow as a result. Wiring and fuses could easily and economically be sized to protect the system from faults in connectivity, backfed shorted panels, charge controller, etc.
Has anyone run into the above considerations in designing an "over-paneled" system?
Then there's the abstract here:
https://ece.northeastern.edu/groups/power/lehman/Publications/Pub2011/2011_9_Zhao.pdf
"This paper focuses on the challenges to overcurrent protection devices (OCPDs) in a PV array under two types of unique fault scenarios. One is a line-line fault that
occurs under low irradiance conditions. In this circumstance, the fault current may not be large enough to trip the OCPDs in the PV array, even when high irradiance occurs later in the day."
My 2s9p arrays would be operating in low irradiance conditions most of the time where I live and smaller fuses mitigate the problem.
Any thoughts and tips would be much appreciated!
-Cal
the NEC does not accommodate highly "over-panelled" solar installations.
I live in a very solar-adverse location. If I did not fear the high likelihood of losing commercial electrical power for a lengthy or indefinite period of time, I would not even consider solar power as anything more than a hobby and curiosity. Since before the last winter solstice, I have been taking output measurements of portable Ecoflow 220W bi-facial panels as well as a pallet of SunPower E-Series: E20-330-COM-MLSD panels. It would behoove me to install the SunPower PVs in two highly over-paneled 2s9p arrays on the roof of my shop to feed my two Ecoflow Delta Pros.
If I were to install small 2s2p arrays, no OCP devices would be required by the NEC, because the arrays would contain only two strings each. On the other hand, a small array isn't really worth installing where I live but 2s9p arrays could support food refrigeration and a well pump but the NEC says they require very large fusing and wire sizes.
The NEC requirements don't make sense to me in the over-paneled 2s9p system, because the worst case currents used in the NEC calculations will never occur with the 2s9p array feeding an Ecoflow Delta Pro SCC (15A / 150V max. solar input) unless there is a fault somewhere and then I would happily welcome under-NEC-spec fuses to blow as a result. Wiring and fuses could easily and economically be sized to protect the system from faults in connectivity, backfed shorted panels, charge controller, etc.
Has anyone run into the above considerations in designing an "over-paneled" system?
Then there's the abstract here:
https://ece.northeastern.edu/groups/power/lehman/Publications/Pub2011/2011_9_Zhao.pdf
"This paper focuses on the challenges to overcurrent protection devices (OCPDs) in a PV array under two types of unique fault scenarios. One is a line-line fault that
occurs under low irradiance conditions. In this circumstance, the fault current may not be large enough to trip the OCPDs in the PV array, even when high irradiance occurs later in the day."
My 2s9p arrays would be operating in low irradiance conditions most of the time where I live and smaller fuses mitigate the problem.
Any thoughts and tips would be much appreciated!
-Cal