After ten years in service my AGM batteries gave up the ghost and I switched to SOK LiFePO batteries.
I would like to share my experience in setting up LIPO batteries and get some opinions on my settings.
Some info about my system and how it’s used.
Two Outback Radian GS8048 inverters (not the 8048A model)
Three Outback flexmate FM80 150VDC charge controllers
Two Outback GSLC load centers
Outback Mate3 system controller
Flexnet-DC
IBR-3-48-175 battery rack
Six SOK SK48v100-NCBT batteries ,48V/100AH each https://www.currentconnected.com/produc ... e-battery/
8.25 KW installed solar panels.
The system is grid tied and batteries are only used during a power outage. Power outages are not common so the batteries spend >99% of time in float. I tried to optimize my settings for float service with charging via the FM80s/solar panels. I’m located in central Arizona so lots of sun and I produce more power than I use on a yearly basis. I have net metering so selling to the grid is a break even proposition.
Installation and power up.
When received the SOK batteries BMS is off so I needed to provide 48V to the terminals to wake up the BMS. Simple to do, just jump the SOK terminals to the old AGM stack.
After wiring the SOK batteries in the IBR battery rack, 2 batteries per 175A breaker, I needed to power up the Radian inverters. At this point the system was powered down with all loads/inputs removed via the circuit breakers. I was aware of the large inrush current the Radians will draw on start up, this can cause the batteries to trip, so I used the method suggested by the SOK vendor, Current Connected. A 40watt 48VDC light bulb was used as the charge limiting resistor.
With the battery and IBR breakers in the off position I connected the bulb across one of the three 175A breakers installed on the IBR battery rack acting as a “jumper”. I then flipped the two battery breakers to on and powered up the first Radian by throwing both battery breakers on the GSLC load center. Unfortunately this did not work. The bulb flickered and the inverter would not power up.
I guessed the inverter needed more that the ~40 watts is was getting for power up so I needed a higher wattage resistor. I purchased a 1.5KW 48V water heater element https://www.amazon.com/dp/B01GPSL6IU?ps ... ct_details and wired it as per the light bulb. This worked with the inverter starting without issue. I then closed the 3 IBR breakers on the battery rack and turned on the second Radian. The water heater element worked perfectly and was a cheap ‘power resistor” for $32.
The settings I used for SOK batteries.
Radian settings
Absorb Voltage and Time 56.8 V / 0.1 hr
Float Voltage and Time 55.2/0hr
Re-float Voltage 51.2V
Re-bulk Voltage 48.8V not adjustable
AC Charger Limit (AAC) 30a
Low Battery Cutout 48 V
LBCO Delay 5 min not adjustable
Low Battery Cut-in 50V
High Battery Cutout 68v not adjustable
HBCO Delay Not adjustable
High Battery Cut-in <68V not adjustable
Sell_RE Voltage 54V
Charge Controller settings
Absorb Voltage 57.2V/0.1hr
Float Voltage 55.2V
Re-bulk Voltage 51.2v
DC Current Limit 80
Absorb End Amps 0A
FN-DC settings
Battery Ah 600
Charged Voltage 56.2V/5 min
Charged Return Amps 12A
Battery Charge Efficiency 98.00%
After running for a week the system is working normally. It goes thru a short MPPT bulk phase at sunrise then GT sell for the rests of the day. At night the batteries BMS shows all 6 units at 99-100% SOC and the 16 individual cells are at <0.01V differential voltage, nicely balanced, and open circuit voltage at 53.25V by DVM @ battery terminals (BMS shows 53.33V)
During the day with up to ~6-7KW of sell power into the grid the individual cells are at <0.15V differential voltage with in/out amps fluctuating at ~ 2-3A per battery. Voltage is ~55-55.4V in sell mode as reported by the FNDC.
I have not cycled the batteries but will do so soon.
I would appreciate any comments on my set up and suggested changes/improvements.
I would like to share my experience in setting up LIPO batteries and get some opinions on my settings.
Some info about my system and how it’s used.
Two Outback Radian GS8048 inverters (not the 8048A model)
Three Outback flexmate FM80 150VDC charge controllers
Two Outback GSLC load centers
Outback Mate3 system controller
Flexnet-DC
IBR-3-48-175 battery rack
Six SOK SK48v100-NCBT batteries ,48V/100AH each https://www.currentconnected.com/produc ... e-battery/
8.25 KW installed solar panels.
The system is grid tied and batteries are only used during a power outage. Power outages are not common so the batteries spend >99% of time in float. I tried to optimize my settings for float service with charging via the FM80s/solar panels. I’m located in central Arizona so lots of sun and I produce more power than I use on a yearly basis. I have net metering so selling to the grid is a break even proposition.
Installation and power up.
When received the SOK batteries BMS is off so I needed to provide 48V to the terminals to wake up the BMS. Simple to do, just jump the SOK terminals to the old AGM stack.
After wiring the SOK batteries in the IBR battery rack, 2 batteries per 175A breaker, I needed to power up the Radian inverters. At this point the system was powered down with all loads/inputs removed via the circuit breakers. I was aware of the large inrush current the Radians will draw on start up, this can cause the batteries to trip, so I used the method suggested by the SOK vendor, Current Connected. A 40watt 48VDC light bulb was used as the charge limiting resistor.
With the battery and IBR breakers in the off position I connected the bulb across one of the three 175A breakers installed on the IBR battery rack acting as a “jumper”. I then flipped the two battery breakers to on and powered up the first Radian by throwing both battery breakers on the GSLC load center. Unfortunately this did not work. The bulb flickered and the inverter would not power up.
I guessed the inverter needed more that the ~40 watts is was getting for power up so I needed a higher wattage resistor. I purchased a 1.5KW 48V water heater element https://www.amazon.com/dp/B01GPSL6IU?ps ... ct_details and wired it as per the light bulb. This worked with the inverter starting without issue. I then closed the 3 IBR breakers on the battery rack and turned on the second Radian. The water heater element worked perfectly and was a cheap ‘power resistor” for $32.
The settings I used for SOK batteries.
Radian settings
Absorb Voltage and Time 56.8 V / 0.1 hr
Float Voltage and Time 55.2/0hr
Re-float Voltage 51.2V
Re-bulk Voltage 48.8V not adjustable
AC Charger Limit (AAC) 30a
Low Battery Cutout 48 V
LBCO Delay 5 min not adjustable
Low Battery Cut-in 50V
High Battery Cutout 68v not adjustable
HBCO Delay Not adjustable
High Battery Cut-in <68V not adjustable
Sell_RE Voltage 54V
Charge Controller settings
Absorb Voltage 57.2V/0.1hr
Float Voltage 55.2V
Re-bulk Voltage 51.2v
DC Current Limit 80
Absorb End Amps 0A
FN-DC settings
Battery Ah 600
Charged Voltage 56.2V/5 min
Charged Return Amps 12A
Battery Charge Efficiency 98.00%
After running for a week the system is working normally. It goes thru a short MPPT bulk phase at sunrise then GT sell for the rests of the day. At night the batteries BMS shows all 6 units at 99-100% SOC and the 16 individual cells are at <0.01V differential voltage, nicely balanced, and open circuit voltage at 53.25V by DVM @ battery terminals (BMS shows 53.33V)
During the day with up to ~6-7KW of sell power into the grid the individual cells are at <0.15V differential voltage with in/out amps fluctuating at ~ 2-3A per battery. Voltage is ~55-55.4V in sell mode as reported by the FNDC.
I have not cycled the batteries but will do so soon.
I would appreciate any comments on my set up and suggested changes/improvements.