Hello,
I am facing a problem with my current set.
Setup:
Deye 5kW inverter
Only GRID port connected
No Battery is available. The option "No Battery" is selected in Battery settings page.
Lower voltage limit of grid is 170 Volts, Upper voltage is 260 Volts
Lower frequency limit of grid is 47.5 Hz, Upper frequency is 52.5 Hz.
The inverter operates as on-grid only and feeds back power to grid.
Problem:
If the grid voltage is less than 210 Volts and the inverter was originally offline, the inverter tries to connect and as soon as it connects it quickly disconnects with F56 fault. This scenario keeps on repeating and with the same result. Even though the grid voltage is within the tolerances settings, it doesn't connect with this weird alarm. Note that this happens even in the middle of the day with sunshine on the panels so irradiance is not an issue.
Normal situation:
When the grid voltage is above 210 Volts, lets say 215V.. 220V.. 225V.. etc, the inverter connects to grid normally and smoothly and operates properly and stays connected even if the voltage drops below 210 Volts as long as it is within the tolerances.
Appreciate your opinions
Thank you
I am facing a problem with my current set.
Setup:
Deye 5kW inverter
Only GRID port connected
No Battery is available. The option "No Battery" is selected in Battery settings page.
Lower voltage limit of grid is 170 Volts, Upper voltage is 260 Volts
Lower frequency limit of grid is 47.5 Hz, Upper frequency is 52.5 Hz.
The inverter operates as on-grid only and feeds back power to grid.
Problem:
If the grid voltage is less than 210 Volts and the inverter was originally offline, the inverter tries to connect and as soon as it connects it quickly disconnects with F56 fault. This scenario keeps on repeating and with the same result. Even though the grid voltage is within the tolerances settings, it doesn't connect with this weird alarm. Note that this happens even in the middle of the day with sunshine on the panels so irradiance is not an issue.
Normal situation:
When the grid voltage is above 210 Volts, lets say 215V.. 220V.. 225V.. etc, the inverter connects to grid normally and smoothly and operates properly and stays connected even if the voltage drops below 210 Volts as long as it is within the tolerances.
Appreciate your opinions
Thank you