Hedges, I saw those MC fuse holders the other day online. That would be the way to go.
Yeah the 5-way connectors will probably never get used. Bought them some time ago.
You may not need the fuses either.
But considering that picture you identify yourself by, there are two situations where fusing the panels might be necessary:
1) Three or more PV strings, and one has a short so the other two dump current into it.
2) The inverter has a fault which dumps battery current into the PV array, and there is a short in the array. (Even the #6 wire could be at risk in this case, so an additional fuse at the inverter end as well would be best.)
Is your battery fused? Since the inverter is rated 1kW, nominal current from 12V battery is around 80A. The fuse would be a bit larger to handle surges. Even though #6 can't carry 100A or more for an extended time, it is enough to serve as ground wire for a 200A breaker, which it can trip in case of a fault.
I think my grid-tie inverters were designed to be safe from having grid current dumped into them due to a fault, but even if not, the AC breaker on my smaller inverters has a suitable rating. The breaker for my larger inverters is too large for that, but I have a combiner box with touch-safe fuse holders for those PV strings.
You could do a twice/year seasonal tilt adjustment of the panels to maximize winter & summer production. With only about 150 pounds total of panels, not very difficult. Mine is about 20x that, so on very substantial and completely fixed mounts.