Hello, this will be my first post but I have been trying to read as much as I can. I have a plan to install a 23kw grid tie system that will power two homes. Here in PA we have virtual net metering so to my understanding we will take the solar to one house and the excess will offset the power in the 2nd home as long as they are both in the same persons name for the electric bill. I plan on using 50 480W panels. I want to install them at about 28 to 30 degrees from what I found on PV watts unless someone else has something to say. I question this myself because my latitude is around 41.45 degrees. The though I am having is because this is grid tie, this will give me the best output through the year.
If I can find them I would like to use two 12.5kw Fronius inverters and tie 2 string on each inverter. Here is where I would like some input. From the two inverters, I am not sure what to do next. I have a run of about 250'. Is there a way to combine the two inverters in a junction box or a breaker box or does this mess with the phasing or not allowed due to some code? If I do this, I assume I would double the amps from a max of 52A up to 104A. I would also have to go with a heavier gauge wire. If I am unable to do this, I will just run the 3 wires from each inverter to a fused AC disconnect near by main meter and then do a line side connection. By combining them I would only have to run 3 wires the 250' vs 6. Due the the gauge of wire, I am not sure of the cost savings if any at this point, hence why I am asking if I can even do this. I have a 200amp panel so I would be unable to tie into it due to the 120% rule.
If you are able please help me determine the best and most effective way to get from the inverter to the grid that would help me a lot. Is the fused disconnect an acceptable idea to protect the system or do I use breakers instead of the fuses? The inverters require an 80A over current protection device. Thanks for your help and I appreciate reading all the comments out there.
If I can find them I would like to use two 12.5kw Fronius inverters and tie 2 string on each inverter. Here is where I would like some input. From the two inverters, I am not sure what to do next. I have a run of about 250'. Is there a way to combine the two inverters in a junction box or a breaker box or does this mess with the phasing or not allowed due to some code? If I do this, I assume I would double the amps from a max of 52A up to 104A. I would also have to go with a heavier gauge wire. If I am unable to do this, I will just run the 3 wires from each inverter to a fused AC disconnect near by main meter and then do a line side connection. By combining them I would only have to run 3 wires the 250' vs 6. Due the the gauge of wire, I am not sure of the cost savings if any at this point, hence why I am asking if I can even do this. I have a 200amp panel so I would be unable to tie into it due to the 120% rule.
If you are able please help me determine the best and most effective way to get from the inverter to the grid that would help me a lot. Is the fused disconnect an acceptable idea to protect the system or do I use breakers instead of the fuses? The inverters require an 80A over current protection device. Thanks for your help and I appreciate reading all the comments out there.