Safely using MCB (mini circuit breakers) for PV & Bi-Directional Battery Protection

That's not a breaker, it's an isolator.
You sure about that???? Why do you think that?

The manufacturer specifically refers to it as an MCB - see the picture below, and specifications attached. It even has a trip curve in the specs. I also use Z Beny's larger moulded case breakers for my batteries.

In my use case its used as an isolator for a fused combiner box, each positive and negative of each string is individually fused. My batteries also have T class fuses, and a breaker. I also have these MCB's between the busbar and MPPT's.

Z Beny is one of the few manufactures that appear to specifically mention no polarity and that they are for PV, hence there is no + or - marked on the diagram.

BB1-63.jpg
 

Attachments

  • DC-circuit-breaker-BB1-63-datasheet-IEC-2021-BENY-New.pdf
    2.7 MB · Views: 9
You're right, I thought it was just an isolator because of the symbol on the front. I didn't realized you had different symbols; here the symbol looks like this:
disj.png

The square and rounded parts indicate it's a thermal-magnetic breaker.

Sorry for the confusion :rolleyes:
 
@BiduleOhm To be honest apart from the switch part of the diagram I've got no idea what the other symbols mean, I just ordered what I considered was appropriate parts going by the manufacturers description, well the second time round anyway.
 
Personally, the question I ask myself is at how many amps the thermal protection will come into operation.

Regarding the MCCB TOMZN I don't even know its trip curve.
Is it B, C or D?
No technical information which is a shame.

Even in the case of curve B we can imagine that a MCCB of 100A will not trigger before perhaps 300A.

Below is an interesting article on the subject.


Edit : TOMZN's answer, "should be" a C curve ?

That said, this does not matter in my opinion, the cables must be sized to support the maximum power of the solar charge controller and the inverter, it could never be greater. The usefulness of this breaker will therefore be to be able to isolate part of the system (I use it for my battery) and above all to interrupt a short circuit which the magnetic part will do instantly. On the other hand, for the thermal part, you will probably never see it trigger in the event of over-current.
 
Last edited: