8800 ÷ 48 =184.4 so 193amp breaker if you can find one if not 200amp, wire calc with a 3% drop at 2meter runs says AWG4/0 so 107mm² which seems madness lemme check a decent source
So as I said earlier 193amp breaker if you can get it if not 200amp and cable is awg0000 which somehow comes to 107mm² but in UK cable terms it would be 35mm² cable at 2 meter lengths.
Edit: Also I'd suggest getting a 200 amp class-t fuse and a isolation switch instead of the breaker, yes it's consumable in the event of over-current but it works much faster therefore safer than a breaker.