I started my sizing project with a 30kWh system. Now I'm doubling it to about 60kWh. I'll be in the countryside but will have access to the internet via t-moble. I'm a software devops person so I run a somewhat substantial homelab that'll draw some load. BTW, location is in Washington County, Texas. Open field, no shade, ground mount system and about 30' away, a covered/shaded 20' container to hold the equipment.
Something I can't quite understand is STC or NMOT? I've based the calcs on NMOT to be conservative, but in some of my calcs it runs the panel count up over 100. So some guidance there would be helpful.
In this setup I plan to use the new (coming soon) REC420AA-PURE-2. I was working with the specs of the REC420AA-PURE-R but they seem to have been bought up.
Finally, spoiler alert, I used chatgpt to run some of these numbers, but garbage in, garbage, out. Don't blame chatgpt if these numbers are crazy, because I gave it the info.
Thanks,
Chris.
So, the rated array value would be: 19.2 kW.
Since the battery bank capacity is about 62.4 kWh, this configuration will cover most of the required energy even in December, the worst month for irradiance. The generator would be used to cover what's missing.
Inverter Specifications:
To account for colder weather, check that the VOC of the panels does not exceed the maximum input voltage of the MPPT charge controllers. Calculating the maximum VOC for each configuration at -10°C (14°F):
Something I can't quite understand is STC or NMOT? I've based the calcs on NMOT to be conservative, but in some of my calcs it runs the panel count up over 100. So some guidance there would be helpful.
High Level Summary
- Solar Panels: 60 REC420AA-PURE-2 panels
- Power Output: 19.2 kW (60 panels * 320W)
- String Configuration: 2 panels per string
- Voltage per String (VMPP): 94.2V
- Current per String (IMPP): 6.88A
- Total Number of Strings: 30 strings
- Combiner Boxes: 6 combiner boxes, each handling 5 strings
- Voltage: 94.2V
- Current: 34.4A
- Inverters: 3 EG4 6000XP inverters
- Each Inverter:
- MPPT 1: 94.2V, 34.4A (Combiner Box 1, 3, or 5)
- MPPT 2: 94.2V, 34.4A (Combiner Box 2, 4, or 6)
- Total Input Power per Inverter: 3.24kW per MPPT * 2 = 6.48kW per inverter (well within the 8kW MPPT capacity)
- Total AC Output Capacity: 18kW (6kW per inverter * 3 inverters)
- Each Inverter:
- Battery Bank: 13 x 48V 100Ah batteries
- Total Capacity: 62.4kWh (48V * 1300Ah)
In this setup I plan to use the new (coming soon) REC420AA-PURE-2. I was working with the specs of the REC420AA-PURE-R but they seem to have been bought up.
Finally, spoiler alert, I used chatgpt to run some of these numbers, but garbage in, garbage, out. Don't blame chatgpt if these numbers are crazy, because I gave it the info.
Thanks,
Chris.
REC420AA-PURE-2 Panel Specifications
NMOT Values:- Power at MPP (PMPP): 320W
- Short Circuit Current (ISC): 8.68A
- Open Circuit Voltage (VOC): 46.0V
- Current at MPP (IMPP): 6.88A
- Voltage at MPP (VMPP): 47.1V
- Panel Efficiency: 21.7%
Rated Array Value
Total Array Power = 60 panels * 320W = 19,200WSo, the rated array value would be: 19.2 kW.
Energy Generation
Using the average daily irradiance, worst case, for December (3.1 kWh/m²/day):- Daily Output per Panel in December:
- Total Daily Output for 60 Panels in December:
Since the battery bank capacity is about 62.4 kWh, this configuration will cover most of the required energy even in December, the worst month for irradiance. The generator would be used to cover what's missing.
Optimal String Count and Combiner Boxes
String Configuration:- Panels per String: 2
- Voltage per String (VMPP): 47.1V * 2 = 94.2V
- Current per String (IMPP): 6.88A
- Total Number of Strings: 60 panels / 2 panels per string = 30 strings
- Combiner Boxes: To evenly distribute the strings and optimize for the 3 inverters, 6 combiner boxes with 5 strings each can be used.
Inverter Configuration with 3x EG4 6000XP Inverters
Each EG4 6000XP inverter has 2 MPPT inputs. Each MPPT input will be connected to one combiner box, ensuring that each inverter handles PV input from 2 combiner boxes.Inverter Specifications:
- AC Input Voltage: 120/240VAC
- Max. AC Input Power: 9000W
- AC Output Voltage: 120/240VAC
- Nominal Power Output: 6000W
- Surge Capacity: 12,000W for approximately 3.5 seconds, 11,000W for approximately 5 seconds
- PV Input Data:
- Number of MPPTs: 2
- Max Usable Input Current: 17A per MPPT
- Max Short Circuit Input Current: 25A per MPPT
- DC Input Voltage Range: 100-480V
- MPP Operating Voltage Range: 120-385V
- Max Utilized Solar Power: 8000W (4000W per MPPT)
- Battery Data:
- Max Discharge Current: 140A
- Max Charge Current: 125A
- Nominal Voltage: 48V
- Inverter 1:
- MPPT 1: Combiner Box 1 (5 strings, 34.4A)
- MPPT 2: Combiner Box 2 (5 strings, 34.4A)
- Inverter 2:
- MPPT 1: Combiner Box 3 (5 strings, 34.4A)
- MPPT 2: Combiner Box 4 (5 strings, 34.4A)
- Inverter 3:
- MPPT 1: Combiner Box 5 (5 strings, 34.4A)
- MPPT 2: Combiner Box 6 (5 strings, 34.4A)
Safety Margins and Cold Weather Implications
Temperature Coefficient of VOC: -0.29%/°CTo account for colder weather, check that the VOC of the panels does not exceed the maximum input voltage of the MPPT charge controllers. Calculating the maximum VOC for each configuration at -10°C (14°F):
VOC Increase Calculation
- Standard Test Condition (STC) Temperature: 25°C
- Temperature Difference: -10°C - 25°C = -35°C
- VOC Increase: VOC * (1 + (Temperature Coefficient * Temperature Difference))
- Panel VOC: 46.0V
Maximum VOC per String Configuration
- 2 Panels in Series:
- VOC per String at -10°C = 50.67V * 2 = 101.34V
MPPT Capacity of Each Inverter
Each EG4 6000XP inverter's MPPT can handle:- Maximum DC Voltage: 480V
- Maximum Current: 17A per MPPT (usable input current)
- Maximum Power Input: 8kW per MPPT
- Input Voltage per MPPT: 94.2V (VMPP)
- Maximum Input Voltage per MPPT (at -10°C): 101.34V
- Input Current per MPPT: 34.4A
- Power Input per MPPT: 94.2V * 34.4A ≈ 3.24kW (well within the 8kW capacity)
Battery Configuration
- Batteries: 13 SOK 48V 100Ah PRO Server Rack Batteries
- Total Battery Capacity: 48V * 1300Ah = 62.4kWh