The factory default value of 105 on Charge DC alarm and DCA in SOK, result in CCL and DCL to be 160 in Victron, setting those value to 60 in SOK result in 100 ON Victron CCL and DCL. (Jakipeer batteries show the right value)
1. Is this a bug in the firmware?
2. Why is cell voltage protect set to 3.70 by default, when the maximum for the batterie is 3,65V?
3. Why is charge DC Protect set to 110 by default when the maximum is 100A for the cells?
This is the answers I got from SOK Europe that does not make any sence to me:.
"For battery cell overvoltage protect, yes 3.65V is written in spec.
When the battery reach 3.65v, the battery will be charged by constant current and constant voltage, and the constant voltage up to current is 0.05C.
Our battery pack is charged in the current close to 0.2C, and then voltage will reach 3.7V. The charging will be stop.
This is the way call “Standard charge method”, 0.5C constant current charge to 3.65v for cell, then switch to constant voltage charge until charge current declines to 0.05C.
The cell Maximum charge current (continuous) is 100A.
Which means that it can be charged continuously at 100A from SOC 0 until the voltage reaches the cut-off voltage.
There is no problem with charging this current for a short time, and no need to worry that it will damage the battery.
1. Is this a bug in the firmware?
2. Why is cell voltage protect set to 3.70 by default, when the maximum for the batterie is 3,65V?
3. Why is charge DC Protect set to 110 by default when the maximum is 100A for the cells?
This is the answers I got from SOK Europe that does not make any sence to me:.
"For battery cell overvoltage protect, yes 3.65V is written in spec.
When the battery reach 3.65v, the battery will be charged by constant current and constant voltage, and the constant voltage up to current is 0.05C.
Our battery pack is charged in the current close to 0.2C, and then voltage will reach 3.7V. The charging will be stop.
This is the way call “Standard charge method”, 0.5C constant current charge to 3.65v for cell, then switch to constant voltage charge until charge current declines to 0.05C.
The cell Maximum charge current (continuous) is 100A.
Which means that it can be charged continuously at 100A from SOC 0 until the voltage reaches the cut-off voltage.
There is no problem with charging this current for a short time, and no need to worry that it will damage the battery.