Having some issues with the MakeSkyBlue controller I am using on my new setup.
I was using the MakeSkyBlue about two years, and was on lead acid battery bank. 2 months ago I assembled a 8 cell, LIFEPO4 bank, for 24 volts, 272 amp cells. It seems to work fine, and I noticed many times during the day I was getting about 450 watts, on my 630 available, and was hitting 28.8 volts on bank usually in a few hours in the morning.
A few days ago, I installed a second bank, a 8 cell 310 amps bank, which was tested to be about 291 amp cells, in parallel. I noticed the controller would not go above about 120 watts on this setup. If I take out the fuse to the panel, it will jump for about 30 seconds to 400 watts, and then work it way down to about 120.
So today, I took charger off the banks in parallel, and patched a wire to the total positive individually, one at a time, and it made no difference, still 120 watts no matter which bank.
Then I took them out of parallel, by disconnecting them at the common terminal, and then tried to charge one bank with them connected at common only. No change.
So I suspect this controller does not like the negative load in its programming. So I am looking for any recommendations, on a good solar charger, that would have no problem handling two LifePO4 banks, totaling 560 amps, 24V.
For panels I have two on my roof of my camper, 2 x 315, for 630 watts on one string incoming feed in parallel, and a third 315 on the front of the truck that I bring in separate, so having two PV inputs would be a plus since the front panel can get shaded time to time.
I use two daly BMS's and I did this on purpose so I had redundancy in case of failure, where I could revert to on bank in an emergency, etc.
A video walk through if interested is here. As said, if any of you are using a controller on more than one bank, of high capacity, would love to hear the model.
I was using the MakeSkyBlue about two years, and was on lead acid battery bank. 2 months ago I assembled a 8 cell, LIFEPO4 bank, for 24 volts, 272 amp cells. It seems to work fine, and I noticed many times during the day I was getting about 450 watts, on my 630 available, and was hitting 28.8 volts on bank usually in a few hours in the morning.
A few days ago, I installed a second bank, a 8 cell 310 amps bank, which was tested to be about 291 amp cells, in parallel. I noticed the controller would not go above about 120 watts on this setup. If I take out the fuse to the panel, it will jump for about 30 seconds to 400 watts, and then work it way down to about 120.
So today, I took charger off the banks in parallel, and patched a wire to the total positive individually, one at a time, and it made no difference, still 120 watts no matter which bank.
Then I took them out of parallel, by disconnecting them at the common terminal, and then tried to charge one bank with them connected at common only. No change.
So I suspect this controller does not like the negative load in its programming. So I am looking for any recommendations, on a good solar charger, that would have no problem handling two LifePO4 banks, totaling 560 amps, 24V.
For panels I have two on my roof of my camper, 2 x 315, for 630 watts on one string incoming feed in parallel, and a third 315 on the front of the truck that I bring in separate, so having two PV inputs would be a plus since the front panel can get shaded time to time.
I use two daly BMS's and I did this on purpose so I had redundancy in case of failure, where I could revert to on bank in an emergency, etc.
A video walk through if interested is here. As said, if any of you are using a controller on more than one bank, of high capacity, would love to hear the model.