I purchased an Eg4 6000xp off grid inverter. I am using one inverter. This discussion is about one inverter for now.
I would like to supply a maximum of power, amps, voltage according to the specs of this inverter.
Without cost concerns, what advise do you have toward actual solar panels that are available to purchase?
I have narrowed it down to these two (but not set and limited to this choice...these are available to me, to pick up at anytime. Others would have to be shipped and I'm not available day to day to inspect a delivered shipment for the damage of panels.):
Silfab - 400 HC+
Silfab - 410 HC+
In order to reach maximum Amps, I would like to take X2, 9-10 panels in series then parallel those two strings to reach a higher Amperage.
So, 9 to 10 panels ... 9s2p/10s2p.
Is this possible? Wise? I'm most worried about overage on volts (over 480v will damage inverter) and if there is too much Amperage with a 20Amp 'Series Fuse Rating'. (Does that even apply here?)
Specs follow:
9/10 panels of the 400
STC. NOTC.
Pmax. 3600w/4000w 2682w/2980w
Vpmax. 324.5v/360.5v 301.5v/335v
Ipmax. 22.2A 17.8A
Voc. 387.2v/363.2v 430.2v/403.5v
SFR. 20A. 20A
9/10 panels of the 410
STC. NOTC
Pmax. 3690w/4100w 2754w/3060w
Vpmax. 350.9v/389.9v 326.2v/362.4v
Ipmax. 21.04A 16.86A
Voc. 410.3v/455.9v 382.1/427.6v
SFR. 20A. 20A
I have researched enough to understand the dynamics of sun,shade,time of day, angle to panel ratios...
I'm interested in the relationship between equipment and power input according to these specifications.
According to these specs, If clipping is not 'dangerous', I do not mind 'losing' any power here or there.
I have an south facing, open sky, mild/chilly winters to min of 10°f (though rare), hot summers to just over 100°f (2 to 3 weeks max).
Will this input damage the inverter?
Does anyone using the Eg4 6000xp a have a more efficient solar panel setup close to maxing out the inverter?
Thanks in advance for your efforts toward helping me out.
I would like to supply a maximum of power, amps, voltage according to the specs of this inverter.
Without cost concerns, what advise do you have toward actual solar panels that are available to purchase?
I have narrowed it down to these two (but not set and limited to this choice...these are available to me, to pick up at anytime. Others would have to be shipped and I'm not available day to day to inspect a delivered shipment for the damage of panels.):
Silfab - 400 HC+
Silfab - 410 HC+
In order to reach maximum Amps, I would like to take X2, 9-10 panels in series then parallel those two strings to reach a higher Amperage.
So, 9 to 10 panels ... 9s2p/10s2p.
Is this possible? Wise? I'm most worried about overage on volts (over 480v will damage inverter) and if there is too much Amperage with a 20Amp 'Series Fuse Rating'. (Does that even apply here?)
Specs follow:
9/10 panels of the 400
STC. NOTC.
Pmax. 3600w/4000w 2682w/2980w
Vpmax. 324.5v/360.5v 301.5v/335v
Ipmax. 22.2A 17.8A
Voc. 387.2v/363.2v 430.2v/403.5v
SFR. 20A. 20A
9/10 panels of the 410
STC. NOTC
Pmax. 3690w/4100w 2754w/3060w
Vpmax. 350.9v/389.9v 326.2v/362.4v
Ipmax. 21.04A 16.86A
Voc. 410.3v/455.9v 382.1/427.6v
SFR. 20A. 20A
I have researched enough to understand the dynamics of sun,shade,time of day, angle to panel ratios...
I'm interested in the relationship between equipment and power input according to these specifications.
According to these specs, If clipping is not 'dangerous', I do not mind 'losing' any power here or there.
I have an south facing, open sky, mild/chilly winters to min of 10°f (though rare), hot summers to just over 100°f (2 to 3 weeks max).
Will this input damage the inverter?
Does anyone using the Eg4 6000xp a have a more efficient solar panel setup close to maxing out the inverter?
Thanks in advance for your efforts toward helping me out.