CGW_6_Actual
Wolf Wrangler
I have 8 yingli 220w panels (4 east, 4 west but very shallow angle roof, almost flat) on a Tracer 8420 with a pair of eco-worthy lifepo 150ah in series (with an external balancer), the problem Im having is that my SOC in the Solar Guardian app always say between 40% and 70%. These are my current settings, is there something I could do better to actually get full SOC?
Battery Type | User | ||||
Rated Voltage | 24V | ||||
Overvoltage Disconnect Voltage | 29.60V | ||||
Charging Limit Voltage | 29.20V | ||||
Overvoltage Recovery Voltage | 29.20V | ||||
Equalize Charging Voltage | 29.00V | ||||
Bulk Charging Voltage | 29.00V | ||||
Float Charging Voltage | 28.00V | ||||
Bulk Voltage Recovery Voltage | 26.40V | ||||
Low Voltage Recovery Voltage | 25.60V | ||||
Undervoltage Alarm Recovery Voltage | 24.40V | ||||
Undervoltage Alarm Voltage | 24.00V | ||||
Low Voltage Disconnect Voltage | 22.20V | ||||
Discharging Voltage Limit Voltage | 22.00V | ||||
Li-ion Battery Protect | Enable | ||||
Temperature Compensation | 0mV/℃/2V |
Battery Capacity | 150Ah | ||||
Boost Charging Time | 120min | ||||
Equalize Charging Time | 0min |