ricardocello
Watching and Learning
Yes the ESS setpoint is the minimum draw from the grid.
It tries to keep grid consumption there, but can’t always react fast enough.
If you set the grid setpoint to zero, it tries to zero out the power from the grid.
Which sounds great in practice, but you will certainly push back power to the grid occasionally.
So the general recommendation is to keep it at 50 or 100W as a buffer.
If you set it to 1000W, then if a 1000W load switches off, for about a second the grid draw will drop to 0W, but it won’t go negative.
Going negative means the PoCo can detect it.
If the CTs and power meter and control loop were faster, there would be less time in the grid feedback.
The EM530 is the best you can do right now.
It tries to keep grid consumption there, but can’t always react fast enough.
If you set the grid setpoint to zero, it tries to zero out the power from the grid.
Which sounds great in practice, but you will certainly push back power to the grid occasionally.
So the general recommendation is to keep it at 50 or 100W as a buffer.
If you set it to 1000W, then if a 1000W load switches off, for about a second the grid draw will drop to 0W, but it won’t go negative.
Going negative means the PoCo can detect it.
If the CTs and power meter and control loop were faster, there would be less time in the grid feedback.
The EM530 is the best you can do right now.