I have a pack of 32 eve cells 305ah in a 2p16s configuration and I'll be splitting them into 2 x 16s packs with their own box/bms.
Wondering which of these two methods is best for connecting them together.
(I do have a 200a fused disconnect before the inverter connection)

1. Use a solid busbar between the -/+ of the packs and then wire pack 1 positive/pack 2 negative with 2x35mm2 to inverter?
1710844094661.png
2. Wire each pack with 35mm2 cables to inverter and not join the packs together at all?
1710844026485.png
 
Layout and expansion would likely drive wiring.

For 2p batteries, Unless the wires are long, I’m not sure either method is better:
IMG_1509.jpeg
IMG_1507.jpeg
Because of wire routing with 8s2p my pack, I went with method 2, and left the option for a third battery with each separate battery fused and fused again after combined.
1710844882040.png
 
Thank you for the detailed comment.
For now I will only have 2 packs of 16s but will probably expand to 3 later on this year.
As I understand, method 3 is the best but might not be worth it.
My two packs will be max 150a charge/discharge each and if I add a third then 100a each.
Is this a good way to hook up as per method 3 or is it the same as 1. above? (the busbar will be insulated ofc)?

1710857847182.png
 
If it was me I would wire them so one could be removed and serviced while keeping the others operational, JMHO.

I am setting up a system with six 24volt 304ah batteries to start and adding another 4-6 down the road. Each battery has a 200amp breaker and will be wired to buss bar with class T fuse, I will be able to isolate and remove any of the batteries with out turning the system off. Just size the buss bars and wire for your future addition.
 