Joes_Going_Solar
New Member
- Joined
- Jul 2, 2022
- Messages
- 14
I have 4 Victron Multiplus-II 48/5000/70-95 120v inverters, and I have a question about the AC in and out. I will be running in a split phase 240v mode with 2 inverters parallel per hot line, grid feeding the inverters, and inverters feeding a load panel. In the manual it shows the connections which I somewhat understand, but it does not show breakers and placements. So, Here’s what I assume but I would like to reaffirm that assumption. The grid panel has two 2 pole breakers, Neutrals, Ground ETC feeding the 4 inverters, then from inverters to load panel with two more 2 pole breakers, Neutrals, Grounds ETC? Wouldn’t this be circuit breakers in parallel and be against code? Another question, the 48/5000 has a 95A passthrough, so would sizing breakers and conductors for a 95A breaker be proper, or would sizing them smaller since I’m running multiple inverters be better?