Hello!
I recently purchased a WZRELB 48v split phase inverter [1] with the intention of using it for house backup in an emergency. The big sell besides price was that it was split phase and can allegedly be connected to the house panel. There's even a section in the manual about doing that.
However, there's one bit in said section that I'm unclear on.
"If the house neutral wire is combined with the ground, connect the N line with it, leave the G line alone. Do not connect the inverter's G line with the N line together."
Is it saying...
- if the house has a neutral ground bond, don't connect the inverter's ground wire to the ground bar in the panel? That sounds a bit screwy.
or
- if the house has a neutral ground bond, don't bond the inverter's ground and neutral. That makes sense.
There's a video knocking around on YouTube where the guy has connected L1 & L2 to a double pole, N to N and G to G just like you'd expect if you didn't read the manual and well.. it's working fine in the video. I reached out to see if he could clarify a couple of things on his setup. I also reached out to WZRELB. Hoping things don't get lost in translation there.
Any thoughts?
[1] https://www.amazon.com/dp/B0BNPSV3WX/?th=1
Is it saying...
or
Any thoughts?