Please correct my if my line of thinking is incorrect, but I was just going to go grid-tie with backfeed due to the limited amount of hours I can collect.
Best you can do is buy grid-tie PV for $1/watt purchase price, amortizes out to $0.025/kWh over 20 years (declining further if working beyond that.) Compare to your $0.12/kWh rates if you use the watts as produced, or to $0.035 credit for backfeed (which makes oversizing not worthwhile.)
My thought is have batteries to harness overproduction during peak hours and backup when grid fails, and grid-tie with back feed for when I run out of solar due to my limited collection times. Once confirmed that things perform well expand at a later time.
My primary battery concern is to ensure that when grid goes out I can have running water and refrigeration.
Good battery backup system is much more expensive than GT PV.
Low cost hybrid inverters no so much of a premium, but don't know about lifespan.
Small refrigeration and small booster pump easy enough. Well pump is what needs multi-kW, which is why I suggest gas generator and water tank.
I have to review code yet, but yes I believe I will likely have to have UL-1741 as well. I haven't got a good grasp at how much more complicated adding a transformer for split-phase will be.
We've always had to have UL-1741 to backfeed grid.
More recently UL-1741-SA, which allows higher percentage of grid power coming from PV without destabilizing it. If you made a zero-backfeed system that likely wouldn't be needed.
Backfeed is the simplest, even of they gave zero credit.
Sunny Island was developed for 220V market, a good fit for moderate size systems there. For off-grid, a 120/240V transformer would boost U.S. 120V model that to the 240V needed for Sunny Boys. If on-grid, 6.7kW maximum draw or backfeed through relay, and all current lands on one phase of utility, may exceed 120% rule for breaker panel. A second 120/240V transformer on input could fix that. I used multiple Sunny Islands, bigger and more expensive system.
If you want to spend the money (and get federal credit while available), $5800 for 2x SI, however many Sunny Boy, and you can operate lots of stuff off-grid if ever needed. Using Lithium battery, one with compatible BMS is preferred. REC works for DIY battery.
SMA Sunny Island Off-Grid Inverter (SI6048-US-10) | eBay
SMA Sunny Island Inverter (SI6048-10).
www.ebay.com
I will try to find this insolation calculator to see if it provides more detail than the solar calculators I have used so far.
I did see that Sunny Boy has three MPPT channels and I was wondering what the best way to connect 18ish panels to them would be.
Possibly 6 panels in series for each MPPT.
First calculation is Voc of string, adjusted for record cold temperature (may be 16% increase in voltage, more or less.)
So it would be better to place each row of 6 on a channel so shade is equal on all three channels throughout the day? I could get by without optimizers?
Yes if multiple strings wired in parallel into one MPPT.
If single series string of panels per MPPT, no need for optimizers regardless.
If roof mount, RSD may be required. Not needed for ground mount.