Hello friends.
I have China-made 5KW hybrid inverter for 3 years -- Axioma Energy ISMPPT-BF 5000 MPPT.
It is visually similar to Axpert 5KVA inverter / Must 5KVA inverter / etc.
Also it has the same user manual and similar specs.
I guess Axioma Energy is just a localised name for Ukrainian market.
According to the manual, along with utility, it should work with generator.
I have typical 3.2kw gasoline generator with AVR.
I measured with the multimeter that generator stably produces a voltage of 230V without load and with an average load.
The frequency of the produced AC is ~52(+-0.2) Hz.
It works fine when I connect the house directly to it.
When I try to use the generator as AC source for the inverter, the inverter on the dashboard shows that the voltage grows from 250v to 310v++ in seconds and the inverter protection is triggered.
What can be the reason the inverter behaves in such weird way?
I will be grateful for any help.
I have China-made 5KW hybrid inverter for 3 years -- Axioma Energy ISMPPT-BF 5000 MPPT.
It is visually similar to Axpert 5KVA inverter / Must 5KVA inverter / etc.
Also it has the same user manual and similar specs.
I guess Axioma Energy is just a localised name for Ukrainian market.
According to the manual, along with utility, it should work with generator.
I have typical 3.2kw gasoline generator with AVR.
I measured with the multimeter that generator stably produces a voltage of 230V without load and with an average load.
The frequency of the produced AC is ~52(+-0.2) Hz.
It works fine when I connect the house directly to it.
When I try to use the generator as AC source for the inverter, the inverter on the dashboard shows that the voltage grows from 250v to 310v++ in seconds and the inverter protection is triggered.
What can be the reason the inverter behaves in such weird way?
I will be grateful for any help.