I have one 4x Sunny Island system with 405 Ah AGM, a 3x system (3-phase) with worn out 15 year old 100 Ah bank, and will be installing a 2x system.
The cost was 15% of new, which brings it under cost of LiFePO4 based on kWh cycle life.
AGM fits the bill for grid-backup. About 700 cycles to 70% DoD is more than enough for a decade of power failures over its float life. (cycled nightly would be only 2 years.)
If sized for 3 days without sun, would cycle 15% most nights, good for about a decade.
Looks like FullRiver's Gel batteries would do 15 years or so at 15% DoD, approaching the 20 years of FLA forklift batteries.
Lead-acid is good for the 22kW, 33kW, or 44kW surge capability of my various systems. Of course lithium would be too, if BMS sized to handle it. But these are also good for the load-dump of an AC coupled PV system, regardless of battery capacity. AGM can take 5C for a while. Lithium, bank needs to be sized large enough and kept balanced and below 100% to accept load-dump charging.
What I would like is AC coupled lithium battery, keeping lead-acid battery at float, and charging with surplus , as commanded by frequency-watts.
Hoping Sunny Boy Smart Energy does that. Never found out how Sunny Boy Storage charging responds to frequency-watts, only know it has Rule-21 curtailment in