post your settings for each program
particularly 02-maximum charging current
10- operation logic
11-maximum utility charging current
12,13,16,23,26,27
is battery type user? then 32 also
Where are you reading this 60 Watts and 80 Watts you're referring to? PV power?
Your attached white board drawing leaves a lot to be desired. You seem to have drawn diodes connected across two different strings; that is not correct. Most everyone explained bypass diodes are "built-in". Here's a photo:
What panels are you (going to) using? Manufacturer & model number...
NO, NO, NO. Four 12 volt batteries in series is 48 volts. That's where your question started. Wire the 4 batteries in parallel; they'll be 12 volts like your inverter.
You are trying to Parallel operate in single phase?
You have parallel boards, parallel communication cables and current sharing cables installed?
Something like this?
Is program 23 set to PAL on both units?
Have you commissioned the units as Master and Slave?
Have you followed these 6 steps?
seems like you have PV wires connected to charge controller battery terminals.
In series PV voltages add (not currents).
15 amp Square D QO breaker would be good for PV disconnect QO220, 2-pole.
The communists there will soon "hold the production of resources collectively" and reallocate YOUR generator and solar product "to the benefit of equality and strong social communities".
Best of luck.
I believe the maximum DC input voltage for your LV5048 is 145 volts.
Four of your panels in series can produce (4 x 37.6) x 1.2 = 180.5 volts; not good.
1.2 is a low temperature correction factor.
You will have to limit panels to 3 in series (3 x 37.6) x 1.2 =135.5 volts; OK, now.
Your...
Consider pulling the cover off inverter and spray with dielectric grease, if available.
https://www.crcindustries.com/products/dielectric-grease-10-wt-oz-03082.html
OK, you have a RBL-60A solar charge controller, you can connect all 3 batteries in parallel (+ to + to +) and (- to - to -)
you have 1 100 watt PV panel (don't mix panels)
connect like this:
So the poultry hobby consumes 6.4kWh/day
Accounting for losses 8kWh/day
For lead acid batteries divide that by .5, getting 16,000 Watt hours per day
Divide that by battery voltage (hopefully 48V.) getting 334 Ah (amp hours)
Multiply that by how many days you could be without sun, let's say 3.5...