  1. T

    Is this as bad as it looks? (JK-BMS)

    Soldered connection is better than crimped. But if both connections are properly made, the difference isn't enough to matter. The only variable is vibration. Soldered is not recommended in a high vibration situation.
  2. T

    Is this as bad as it looks? (JK-BMS)

    I didn't extend my leads. I planned for the BMS to be next to the battery negative and the breaker to be next to the BMS.
  3. T

    Is this as bad as it looks? (JK-BMS)

    Shrink tubing is fine. But you should either cut that bolt shorter or replace it with a shorter one first.
  4. T

    EG4 18k PV cheaper than signature solar?

    You should have asked Signature Solar if they were an approved vendor.
  5. T

    MASSIVE Overpaneling -MPPT input current

    I used to think this, too. But actually they are the same. (Just more paranoid)
  6. T

    Goal Zero Yeti #300

    Two options 1. The battery is defective and won't accept a charge. Or 2. You're using all produced power during the day, and nothing is left to charge the battery.
  7. T

    Is this as bad as it looks? (JK-BMS)

    There's nothing wrong with soldered connections as long as they are good clean connections. (Everything on every circuit board is soldered) And the 7 AWG silicone insulated conductors are more than capable of handling 100a each, at that short length.
  8. T

    Off-Grid Ground & Victron Lynx

    Either is fine, but the service panel is the simpler option. As it's already designed to accommodate more connections.
  9. T

    Who here has the best dump load management system going on?

    That's over my head. I'm just a simple man, who prefers to keep my projects simple. I avoid electronics whenever possible. I can do anything I need with simple relay logic.
  10. T

    Selling Growatt SPF 3000TL LVM-48P - $400/ea

    Thanks But I'm only interested in the 5000's.
  11. T

    208V 3P 60Hz battery charger for ~51.2V LFP 10kW

    They are expensive. Around $2k. It would be cheaper to buy 3 single phase chargers.
  12. T

    MASSIVE Overpaneling -MPPT input current

    The SCC will never see short circuit current, unless it shorts internally. Which means that the SCC has already failed.
  13. T

    Sizing EGC with no overcurrent device

    Yes No OCP is required. But it is recommended to have a disconnect near the SCC for service.
  14. T

    Sizing EGC with no overcurrent device

    That table is for the current carrying conductors. Use this for the EGC. #10 is still correct, for that low of OCP. Just giving you the correct table.