Sizing EGC with no overcurrent device

Bluedog225

Texas
Joined
Nov 18, 2019
Messages
2,959
I’m noodling a sketch of my system to prepare for installing my grown up arrays.

I don’t know how to size my equipment grounding conductor from the array to the power shed since there doesn’t seem to be a need for an overcurrent protection device in this part of the system.

Any thoughts on this (or my diagram) appreciated.

Thanks

IMG_0781.jpeg
 
I may expand to 4 arrays. Each the same as the two above. That is, each array will have two strings of 7 panels in series and those two strings in parallel.

The fuse rating is 15 amp. if I am reading below correctly. Therefore, for each 7s-2p array 10 awg set of current carrying wires, I’d run an egc rated for 30 amps. That is, another 10 awg wire.

Am I close?

And thanks for helping.



IMG_0783.jpegIMG_0784.jpeg
 
Last edited:
That table is for the current carrying conductors.
Use this for the EGC.


7uqFA.jpg

#10 is still correct, for that low of OCP.
Just giving you the correct table.
 
@timselectric a follow up.

If in ultimately plan 4 arrays needing 15 amps grounding conductor each. So 60 amps.

Two questions:

1. From the Table 250.122 it looks like a 10 awg wire would handle the entire 60 amp grounding conductor requirement. So no need for multiple 10 awg runs. Just the one. Is this right?

2. In the event I add even more arrays, do I need the grounding conductors to be able to handle all arrays simultaneously? Seems like an event that would create the need to safely ground the current would not involve all the arrays at once. Or is that simply the rule and I need to follow it?

Thanks
 
@timselectric a follow up.

If in ultimately plan 4 arrays needing 15 amps grounding conductor each. So 60 amps.

Two questions:

1. From the Table 250.122 it looks like a 10 awg wire would handle the entire 60 amp grounding conductor requirement. So no need for multiple 10 awg runs. Just the one. Is this right?

2. In the event I add even more arrays, do I need the grounding conductors to be able to handle all arrays simultaneously? Seems like an event that would create the need to safely ground the current would not involve all the arrays at once. Or is that simply the rule and I need to follow it?

Thanks
A single EGC is used for all current carrying conductors ran together. And is sized for the largest circuit in the run or grouping.
 
If 15a is the largest circuit. A 14 AWG EGC is all that is required to cover all circuits in a single run or grouping. (Like In a conduit)
 