EG4 Indoor 280Ah 48v WallMount Battery

How close to each other can you install them, to be able to reach in and access the on/off and breaker on the side? The 12" requirement of the older model was pushing me toward server rack style batteries, but if only 3-4" or so required for these, they would sure be a space saver for our new build.

The manual recommends ≥12in separation between batteries.
 
The UL9540 test was done with the batteries and inverters 6 3/4 inches apart. 12 inches in the was put in the manual because most AHJs won't accept less
So you purposefully made the manual requirement harder than what was necessary just to appease some AHJs?

That seems dumb. The manual should be the actual requirements. If an AHJ says 2 ft and you see 6.75 inches in the manual, you have more room to argue for 12 inches.

In other words, you shouldn't pander to the AHJ authority escalation tactics. Put what the product will do in the manual.

Mike C.
 
3 batteries per 18k is the permit/inspection limit, but I don't see why there would be a problem using five batteries per inverter, you could double up the parallel cables between the three inner batteries if that makes you feel better.
 

Attachments

  • 17121585975217282421310720239940.jpg
    17121585975217282421310720239940.jpg
    127.8 KB · Views: 11
3 batteries per 18k is the permit/inspection limit, but I don't see why there would be a problem using five batteries per inverter, you could double up the parallel cables between the three inner batteries if that makes you feel better.
Yeah, or 6 by using two Victron Energy Lynx. Three into one, three into the other, and each Lynx going to the 18.
 
I want to see someone build out 860 kWh of storage lol
I wonder how the internal shunts would work in terms of calculating correct SOC in this case.
Say you pull 100A, it'd only be roughly 1.6A per battery if you had 64 in parallel.
But that's ~5.2kW, which is way above the average draw I'd imagine.
Say your average draw in your house is 500W, you'd have almost no current from each battery.
Can the shunt measure that?

Forum challenge: EG4 should send Will 64 batteries so he can test it out.
 
Last edited:
These wall mount batteries are getting more and more attractive as the prices drop.

I have a good sized shed with a real roof on it that I could easily mount 1-2 of these along with an inverter in. Has enough roof space on it for a few kW of panels. So not having the weatherproofing, but still having the heating elements is basically perfect for this application.
 
Isn't one of the ID specifically reserved for firmware updates? I want to say it's "64", which is actually zero...

ID 64 would be used for firmware updates. However, it can still be used for general communication in this instance.
 
I wonder how the internal shunts would work in terms of calculating correct SOC in this case.
Say you pull 100A, it'd only be roughly 1.6A per battery if you had 64 in parallel.
But that's ~5.2kW, which is way above the average draw I'd imagine.
Say your average draw in your house is 500W, you'd have almost no current from each battery.
Can the shunt measure that?

Forum challenge: EG4 should send Will 64 batteries so he can test it out.

That would be an interesting test for sure!
 
Anxious to see how the spacing between them comes out with the conduit boxes, I can't tell how much the recommended 12" spacing on the outdoor model is code and how much is reasonable access to the side controls. Will seems to want to put them right up next to each other, but the latches on the conduit boxes will require _some_ minimum spacing.
First impressions:
Feet! Love the feet, wish the Outdoor had leveling feet.
Will mentions the fans spooling up in his load test, but that's the inverter, yes? No fans in the battery box, correct?
10% less than the outdoor model is nice, but I'm glad I have the outdoor model on the way.
Overall, very nice, this is the one that I'd put in my FL condo for grid support/UPS. Someday, after I win the lottery. 8*)
Good point on the latches

Yes inverter fans. Not battery

Yeah outdoor rating is pretty good for the price. Won't have to worry about mounting location
 
I really like that the connections have been moved to the top, and the width is a little smaller. My area is pretty cramped, so I really appreciate any extra room I can find. I'm curious that they left the heater in.

I'm glad that EG4 is paying close attention to code compliance. I spent months trying to find a setup that would pass local inspection. At least I won't have to worry about the EG4 products.
 