Overkill BMS connecting Inverter = short circuit! Help!!

did the precharge let a bulb with auto volatage connected for over a minute then after try connecting negative got sort circuit as before .got a friend to bring me an inverter to see if it is inverter or battery apparently it work with his inverter ,do you think the problem is in pic attach .
 

Attachments

  • photo_2023-10-24 09.25.12.jpeg
    photo_2023-10-24 09.25.12.jpeg
    787.1 KB · Views: 15
If bulb remained lit for a minute, then it seems like inverter is shorted.

"Auto voltage" meaning 12V? OK to test for shorts, not sufficient to precharge for 48V battery.
A 120V bulb (or four 12V bulbs in series) would work for 48V.

Friend's inverter works? Or at least precharges until light goes out? But yours does not?
Sounds like your inverter is dead. Did it ever work? Might it have ever been connected backwards?
 
Inverter working all like now just dont recgonize the battery and gets SC when battery connected.It working with Solar now.
 
If bulb remained lit for a minute, then it seems like inverter is shorted.

"Auto voltage" meaning 12V? OK to test for shorts, not sufficient to precharge for 48V battery.
A 120V bulb (or four 12V bulbs in series) would work for 48V.

Friend's inverter works? Or at least precharges until light goes out? But yours does not?
Sounds like your inverter is dead. Did it ever work? Might it have ever been connected backwards?
i am thinking iverter i sshorted
 
I'm not sure of the internal architecture. It appears the battery input is shorted (if light bulb for precharge remains on indefinitely, and battery reports short circuit), but PV to AC path works.

If battery input terminals are different impedance from another identical working unit, that suggests something is wrong. Compare apples to apples, each inverter identically connected (or not) to PV and loads.
 
I'm not sure of the internal architecture. It appears the battery input is shorted (if light bulb for precharge remains on indefinitely, and battery reports short circuit), but PV to AC path works.

If battery input terminals are different impedance from another identical working unit, that suggests something is wrong. Compare apples to apples, each inverter identically connected (or not) to PV and loads.
here is what i use to precharge check pics out, who that have been sufficient
 

Attachments

  • photo_2023-10-24 10.05.31.jpeg
    photo_2023-10-24 10.05.31.jpeg
    503.9 KB · Views: 5
  • photo_2023-10-24 10.05.43.jpeg
    photo_2023-10-24 10.05.43.jpeg
    463.4 KB · Views: 5
Have a DMM or volt meter?
Useful to monitor and diagnose.
 
Can anyone give me the step by step method please of the precharging thank you.
 
Can anyone give me the step by step method please of the precharging thank you.
Can use one of those resistors please thank you.
 

Attachments

  • photo_2023-10-24 13.43.23.jpeg
    photo_2023-10-24 13.43.23.jpeg
    732.6 KB · Views: 11
Here's how to build it into a switch:


All you do with the light bulb is use it to complete circuit between cable terminal and stud. If light glows then slowly goes dim and goes out, time to put terminal on stud.

Sure, those resistors should work. What resistance values?
 
Here's how to build it into a switch:


All you do with the light bulb is use it to complete circuit between cable terminal and stud. If light glows then slowly goes dim and goes out, time to put terminal on stud.

Sure, those resistors should work. What resistance values?
ok it 40 ohms and should i have the inverter in a off position please thanks.
 
Does the inverter have a circuit breaker to turn it off? Or a low power switch.
(My Sunny Island has a circuit breaker which isolates its capacitor bank from input, so I would have to turn that breaker on before precharge.)

Ideally you precharge the capacitor before inverter starts operating. Because it might consume 25 to 50W no-load, which is 0.5A to 1.0A, would prevent complete precharge.

Try with the inverter off. Precharge, observe voltage riding with a meter (may be quick.) Then connect cable if voltage came up. Then turn on inverter.

50V / 40 ohms = 1.25A
1.25A x 50V = 60W

That is OK. If it gets too hot to touch during precharge, there is a short and you need to stop before overheating the resistor. (It is probably rated for 50W or 100W, but needs a heatsink to handle that continuously.)

A 120V 100W lightbulb has its advantages.
 
Here's how to build it into a switch:


All you do with the light bulb is use it to complete circuit between cable terminal and stud. If light glows then slowly goes dim and goes out, time to put terminal on stud.

Sure, those resistors should work. What resistance values?
ok do i have to keep battery breaker and bms off also ?
 
You would turn battery & BMS on. So it supplies power through the resistor to precharge power.

It helps if you understand where current is flowing, and what components do.
I'm just winging it, don't even have a schematic of your circuit.

 
tried all what you said but the light bulb never went off means there is a short on the inverter end.
 
This thread title seemed to fit, so hopefully a good place to start.

Just reinstalled my 280Ah LiFePO4 battery after winter storage, reading very close to 13v no load. Everything was still how I left it in October, SCC, B to B charger and 1600w LF inverter all connected to buss bars only. I tried to switch on the battery via overkill bluetooth, but no go. Just a red "short circuit" message. I tried a few times.


Decided to remove inverter connection from the buss bars; sure enough the battery powered up, house lights came on as did the SCC screen. At first my meter across the 12v +/- inverter connections showed "continuity". Then intermittently it went to reading "open circuit" and short again minutes later.
inverter & battery.JPGInverter and meter.jpg
Now the inverter is on the bench and across the terminals it still reads open. I can't find anything loose to wiggle and bring back the short. This inverter has not skipped a beat since installation 2 years ago, and has seen no excessive loads or physical trauma.

What should the ohm meter read across the low voltage side? Would really appreciate a path forward if anyone has ideas. Thanks.
 
Protects from overcurrent tripping, or blowing fuse or welding contacts or damaging capacitors.
Lots of things can get damaged by multi-thousand amps spikes.
Soft-start circuits are designed into many products, but few have the massive surge of these lithium batteries.
 
What should the ohm meter read across the low voltage side? Would really appreciate a path forward if anyone has ideas. Thanks.

Try giving battery a recharge (With suitable CV/CC supply.)
 
Try giving battery a recharge (With suitable CV/CC supply.)
I don't have a CV/CC supply, just an old school charger for FLA. The battery is receiving solar charge from the SCC as we speak, so I should be able to see if bringing up the voltage helps. Thanks for the suggestion.

Also, just connected the inverter to a FLA deep cycle battery (showing 12.5v unloaded) and I have 115v at the output side. What the hell?
 