Update on 6000XP issue.
Everything is fine unless I combine two strings together in parallel. Either single 5x string is fine for each PV input.
Seeing 2300-2500w per string, if my math is correct 2423w / 190.7v = 12.7a per string.
If two strings in parallel 12.7a x2 = 25.4a hence the PV short fault I am experiencing?
Plan to just wait until the 2nd 6000XP is installed to add back more panels.
I've attached today's history with only 5 panels per PV input.
Time | Status | vpv1 | vpv2 | vpv3 | vBat | soc | ppv1 | ppv2 | ppv3 | pCharge |
2024-04-06 14:11:25 | 0xC0 | 190.7 | 190.8 | 410 | 53.7 | 58% | 2423 | 2424 | 0 | 4574 |
2024-04-06 14:08:23 | 0xC0 | 189.3 | 188.3 | 409.4 | 53.6 | 57% | 2310 | 2313 | 0 | 4387 |
2024-04-06 14:05:21 | 0xC0 | 181.2 | 190.7 | 401.8 | 53.4 | 56% | 1277 | 1219 | 0 | 2026 |
2024-04-06 14:02:16 | 0xC0 | 185.6 | 187 | 408.5 | 53.6 | 56% | 2351 | 2383 | 0 | 4360 |
2024-04-06 13:59:16 | 0xC0 | 189.7 | 187.7 | 399 | 53.4 | 55% | 695 | 345 | 0 | 755 |
2024-04-06 13:56:13 | 0xC0 | 189.2 | 191.4 | 408.7 | 53.5 | 55% | 2313 | 2328 | 0 | 4367 |
2024-04-06 13:53:09 | 0xC0 | 180.7 | 183.3 | 402.2 | 53.3 | 54% | 1489 | 1534 | 0 | 2507 |
2024-04-06 13:50:06 | 0xC0 | 185.3 | 184.6 | 403.5 | 53.5 | 54% | 1624 | 1726 | 0 | 2683 |
2024-04-06 13:47:03 | 0xC0 | 187.3 | 187.9 | 408.1 | 53.5 | 53% | 2244 | 2273 | 0 | 4129 |
2024-04-06 13:44:01 | 0xC0 | 190.8 | 188.8 | 407.9 | 53.5 | 53% | 2215 | 2256 | 0 | 4088 |
2024-04-06 13:40:57 | 0xC0 | 190.8 | 189.7 | 408.4 | 53.5 | 52% | 2301 | 2324 | 0 | 4305 |
2024-04-06 13:37:53 | 0xC0 | 193.3 | 194.2 | 409 | 53.5 | 52% | 2455 | 2470 | 0 | 4616 |