diy solar

diy solar

LED lights ghosting when on solar/inverter, but not when on grid power

Your inverter is putting out some HF noise and the capacitance of the cable is enough to supply power to the LED
Attached are pictures of the LED and some wiring.

The LED only has 2 wires coming in, Live and Neutral

I re-tested things, pertinent points:
- When circuit is connected to grid supply directly there is no glow
- When connected to the inverter, in both inverter and bypass mode, there is a glow
- On bypass mode an N-G bond exists at the main distribution box, and there is 0 V measured between neutral and ground
- I have multiple lamps on two circuits, all lamps in a circuit act the same depending on their power source
- If I swap the power source between grid direct and inverter, the problem swaps as well, the circuit that is being powered by the inverter has the glow, the circuit that is on the grid does not have the glow.

I feel efficientPV's note about HF noise is the only explanation that explains the above? If yes is it something that can be safely ignored?
 

Attachments

  • 1000019920.jpg
    1000019920.jpg
    298.3 KB · Views: 5
  • 1000019921.jpg
    1000019921.jpg
    301.2 KB · Views: 4
  • 1000019922.jpg
    1000019922.jpg
    143.6 KB · Views: 5
  • 1000019923.jpg
    1000019923.jpg
    62 KB · Views: 5
  • 1000019924.jpg
    1000019924.jpg
    62.1 KB · Views: 4
Last edited:
Could you open up your LED light and show what it looks like and show the circuit board it uses? Does it have L, N, and Ground wires or just L and N wires? Edit: I now see images you posted at the same time I wrote this.
 
Last edited:
Could you open up your LED light and show what it looks like and show the circuit board it uses? Does it have L, N, and Ground wires or just L and N wires? Edit: I now see images you posted at the same time I wrote this.
Only L and N wires, which makes me think it can't be current passing to Ground?
 
@ABarbarian What kind of light switch do you have? Is it purely mechanical or electronic? Does it have a glow in the dark light inside?
 
Last edited:
This is what I was thinking is the cause.

 
See pics, yes when glowing there is 0.09 Amps passing through

It could be that case of the either the driver or fixture is grounded to whatever they are mounted to but it doesn't look like that's possible since they both appear to be plastic.

But math and Watts law tells us the you've got current flowing somehow. V x A = W If either V or A = zero then no watts. No watts = no light. We know you've got 115 volts on the neutral.

Regarding your measurement technique: That is a clamp style meter and can't be used to make this measurement. It works by putting the clamp around the wire and most of them are only accurate once they get above 2 or 3 amps.

To get accurate measurements of less than 1 amp (mA range) one needs to use a DVM and run the circuit through it in series. Move the red lead from the V to the A on the meter then select A or mA if your meter has two ranges. I've done a bad job explaining it but I'm sure there's plenty of YouTube videos.

I've tried to show it in the bottom picture.
Cut the wire on at the blue x then use you meter to complete the circuit.

1713178068796.png

1713178530874.png
 
We know you've got 115 volts on the neutral
Just a quick reply: 115 V is Neutral to Ground, but no ground wire is coming into the lamp, roof is cement and conduit plastic so I am confident there is no grounding of the lamp, and current passing across N-G's 115V is not applicable to the glow.

No glow when the circuit is on direct grid supply makes me feel the switch is probably not leaking current through line, and there is no ground, so it feels like there is no traditional circuit here causing Amp flow.

I like efficientPV's theory that the "inverter is putting out some HF noise and the capacitance of the cable", although my understanding of this is near nothing.
 
Just a quick reply: 115 V is Neutral to Ground, but no ground wire is coming into the lamp, roof is cement and conduit plastic so I am confident there is no grounding of the lamp, and current passing across N-G's 115V is not applicable to the glow.

No glow when the circuit is on direct grid supply makes me feel the switch is probably not leaking current through line, and there is no ground, so it feels like there is no traditional circuit here causing Amp flow.

I like efficientPV's theory that the "inverter is putting out some HF noise and the capacitance of the cable", although my understanding of this is near nothing.
So you do have a 2-terminal device? Either your switch isn't isolating enough (try detaching the wires from your switch, cleaning the insulation and ends, and separating them by a few inches, to have a really open circuit), or there's something to the RFI scenario.
 
Looking at pictures of the lamp, why are the probes connected? Current is thru the clamp. Connect brown and blue together and also connected to one leg of power. That would determine if there is leakage to concrete.

Reversing brown and blue would also be an interesting test for leakage.
 
Per my link, I remember reading this elsewhere years ago and always thought this was the reason. My particular setup bonds the neutral and ground in the multiplus but I don't have an actual ground rod to earth. Is it possible to power the LED via induction through 1 conductor? I mean we are talking milliamps of current.
I would test by removing the ground if I was actually at the cabin where this stuff is located but I'm not and won't be for another month.

Probably because one of the ways to make an inexpensive inverter output stage requires the output to be floating.

With a normal AC sine wave of the sort you get from the wall, the “line” terminal swings between -170 and +170 V (for a 120 V RMS circuit), while the “neutral” terminal remains close to the earth or ground terminal - because neutral is actually connected to ground at one point.

You can recreate this in an inverter by generating +170 and -170 V power buses internally, and connecting the output alternately to one of +170, -170, or neutral. With this design, neutral can remain at ground, but you need both polarities of voltage.

A cheaper design is to have just a single 170 V supply, and a floating neutral. During the part of the waveform where line is supposed to be +170 with respect to neutral, transistors connect line out to +170 and neutral out to internal power supply ground. During the portion of the waveform where line is supposed to be -170 with respect to neutral, line out is actually connected to output supply ground, while output neutral is connected to power supply +170.
This requires only one polarity of 170 V power supply, so it’s cheaper, but means that output “neutral” is actually at 170 V with respect to ground for part of each cycle of the output.

It is also possible to create AC at the battery voltage, using only a single polarity of supply, using either a single primary winding and a 4-transistor H-bridge (the 2nd design above), or a center-tapped transformer and 2 transistors. Then the voltage is stepped up to line voltage by the transformer. Since the transformer secondary is isolated, it can be connected with the neutral output grounded. But transformers cost money and also add extra weight.

And that’s probably why you measure voltage on neutral on your inverter: It is probably using an H-bridge type design at line voltage, without a step-up transformer."

Any relevance to our situation?
 
To get accurate measurements of less than 1 amp (mA range) one needs to use a DVM and run the circuit through it in series
I think the attached pictures fix my measuring technique.

When run in series on Neutral getting 0.058 mA
When run in series on Line getting 0.10 mA

Last picture shows if I disconnect the positive the glow remains
If I disconnect negative but connect positive, no glow

Probably not important:
If I connect the incoming negative to the lamps positive and no other connection, have glow
 

Attachments

  • 1000019929.jpg
    1000019929.jpg
    86.7 KB · Views: 1
  • 1000019930.jpg
    1000019930.jpg
    66.9 KB · Views: 1
  • 1000019932.jpg
    1000019932.jpg
    122.9 KB · Views: 1
  • 1000019933.jpg
    1000019933.jpg
    108.7 KB · Views: 1
  • 1000019934.jpg
    1000019934.jpg
    67.8 KB · Views: 1
So you do have a 2-terminal device? Either your switch isn't isolating enough (try detaching the wires from your switch, cleaning the insulation and ends, and separating them by a few inches, to have a really open circuit), or there's something to the RFI scenario.
Switch is a simple mechanical switch

See attached picture, if positive line is broken the glow remains, I believe that eliminates the switch not isolating being the cause?
 

Attachments

  • 1000019934.jpg
    1000019934.jpg
    67.8 KB · Views: 2
Looking at pictures of the lamp, why are the probes connected? Current is thru the clamp. Connect brown and blue together and also connected to one leg of power. That would determine if there is leakage to concrete.

Reversing brown and blue would also be an interesting test for leakage.
I was using an incorrect multimeter in my first set of readings, I think I fixed that. The probes were connected to try and read what Amps were passing through, I just made a post about the results.

"Connect brown and blue together and also connected to one leg of power. That would determine if there is leakage to concrete" - I understand you mean the incoming neutral (blue) connect to the lamps positive (brown), but what is the leg of power? Or do you mean the lamps neutral and positive connect to either incoming line or neutral? And then what do I measure?

"Reversing brown and blue would also be an interesting test for leakage" - I tested different incoming and lamp connections: if the incoming neutral connects to either lamp line or neutral there is glow, anything to lamps positive no glow.
 
So it only glows when neutral is connected (blue). Seems like capacitive coupling from neutral to concrete ceiling. Set your multimeter to AC voltage and measure from LED fixture metal case to neutral. Scrape off a bit of paint to make contact. Start with highest voltage setting and work your way down until you get a reading.
 
This requires only one polarity of 170 V power supply, so it’s cheaper, but means that output “neutral” is actually at 170 V with respect to ground for part of each cycle of the output.

It is also possible to create AC at the battery voltage, using only a single polarity of supply, using either a single primary winding and a 4-transistor H-bridge (the 2nd design above), or a center-tapped transformer and 2 transistors. Then the voltage is stepped up to line voltage by the transformer. Since the transformer secondary is isolated, it can be connected with the neutral output grounded. But transformers cost money and also add extra weight.


And that’s probably why you measure voltage on neutral on your inverter: It is probably using an H-bridge type design at line voltage, without a step-up transformer."

Any relevance to our situation?
I am not sure it is relevant, because the glow persists when inverter is set on bypass mode and there is no voltage difference between N-G, I believe in that situation the inverter is not doing much, it is passing through the grids power (however my issue suggests the inverter or inverter cabling is doing "something" because the glow disappears when powered directly from grid).
 
I am not sure it is relevant, because the glow persists when inverter is set on bypass mode and there is no voltage difference between N-G, I believe in that situation the inverter is not doing much, it is passing through the grids power (however my issue suggests the inverter or inverter cabling is doing "something" because the glow disappears when powered directly from grid).

How does the inverter pass through grid power? Is it a transfer relay? Is it an inverter/charger?

I guess I can look it up.

I'm now very curious about my setup. Haven't had to run the Gen but now very curious if it happens when gen is supplying power.

Thanks for sharing. In my case I'm not worried about anything but very curious why I have the glow.

The only other oddity I have is the gfci will sometimes pop when I shut the ceiling fans off.
 
Back
Top