Reality Check on Building a Family-Sized Home Off-Grid

Only 18K inverters or those with similar capability can be paralleled in this manner so that they comply with 705.13 and Section 706. Again, I want to state clearly that you can't parallel inverters like this UNLESS they have a Power Control System (PCS) that complies with 705.13 and the 18K inverters do (that's why they are all connected with a control cable).
Not sure if you've seen the thread where a pair of 18kpvs went berserk and killed a bunch of appliances when a longer crossover cable was accidentally used for the comms instead of the shorter provided straight cable. Any kind of rodent damage to a straight cable could end up with a similar failure so protect it well.
 
Hello Everyone,

My name is David. I live in NY, and have property in the Adirondacks that I am building on this year. I am - and have been for a few years - weighing whether or not I want to make this an off-grid build. So, I am reaching out to, well, anyone that will give me their experience with off-grid living to help me make that decision.

My energy needs were calculated based on my family's current avg. energy usage - ~30KWhs per day - and I worked with two different solar engineers to spec out a system. Of course, we factored peak sun hours per day, as they historically occur in my property's zip code. Using 3 days of autonomy, at the lowest avg. sun hours per day (in December), the system came out as: 13KW PV array and ~2000AH of LifePo batteries. Just to be safe, though, I purchased 26KWs of Longi bifacials, thus doubling the array size. Of course, we would have a backup generator as well.

The build will be ~1200 sq. ft., and built very tight, with spray foam insulation.

Why am I considering and off-grid build? I do not have a pole to my property - the nearest being ~1 mile away - and the quote is $180-$200K from National Grid. I know this is a lot, and I am sure that most-if-not-all that are reading this - on this forum, in particular - are thinking "That's ridiculous. Solar is a no-brainer." That said, please consider the rest of my considerations:

(i) When not in use, I will be renting the property. Renters are not energy conscious.

(ii) I will be adding more, but smaller, builds to the property in the future for rental purposes.

(iii) I do NOT want to be constantly thinking about energy usage / conservation when I am using it.

(iv) I do NOT want to be working on the array/inverters/batteries regularly.

(vi) Based on early quotes, between hardware and installation, the solar will cost ~$80 - $100K. This is before tax credits.

With that in mind, and despite my best searching/reading efforts on line, I have yet to find anyone - and I mean, NO ONE - that has said something along the lines of "Well, we have X-size array and Y-sized battery bank, and we never have to worry about power. We threw in central air, and have a hot tub, and we never worry about whether the batteries are drawing down." There seems to always be some discussion about raising the thermostat in the summer during a cloudy stretch; fear of installing heat pumps; no one uses central air - all mini-splits; etc.

So, with that as my back drop, is there anyone on the forum that has (i) built a 1200 ft. + house (not a small cabin) that supports a family, and (ii) has installed a large solar/PV system with a battery back up in the North East that has had a smooth experience? What do I mean by "smooth"? The system, (a) for all intents and purposes run itself without frequent inspection/intervention, and (b) the backup generator only runs, say, 5 or 10 times per year.

If, for instance, I were able to install a system for the cost that I've spec'd, and it ran "smoothly", then I'd likely go with the Solar, and could scale up accordingly for the other builds. But, if real world experience - at a larger scale - finds that the generator is often running, and there are semi-frequent-to-frequent interventions necessary, then I'd likely bite the bullet.

Please know that I write this with a true spirit of inquisition, humility and curiosity. I'd love to have a great off-grid system. Who wouldn’t? But I am building this property as an asset, and with future plans in mind, so I want to do it right the first time, even if that means bending over backwards to do so.

Thank you in advance to anyone that will afford me their time.
I think it's staring you right in the face that solar is not for you. If you don't want to worry about it, get grid tied. Solar is not a thing where you can just suck down massive amounts of energy for your hot tub without ever thinking about it. Most people doing off grid setups aren't building large conventional houses. If you need a system that can feed multiple residences, you will spend more on buying it, building it and maintaining it than you will putting power poles in and paying for grid power for decades. Remember, this stuff doesn't last forever and will need to get replaced at some point. Also, you live in New York. Your government may complicate things.
 
Not sure if you've seen the thread where a pair of 18kpvs went berserk and killed a bunch of appliances when a longer crossover cable was accidentally used for the comms instead of the shorter provided straight cable. Any kind of rodent damage to a straight cable could end up with a similar failure so protect it well.
That was a crazy thread.
 
I put in an openevse charger., I have two EV's. This would be the one thing that could be a big wrench, however I would provide the charger and connect it up like I do, to a control and make it part of the rental agreement you may only use the provided L2, it may not provide consistent output but will give you any overproduction available. I'd give guidance for daytime charging and bill if you detect an EV type load to cover the generator/propane. I went a little beyond, scripted /controlled so mine only allows charging when the solar batteries are at specific target SOC's, and ramps up the rate as long as I am at the target. Currently my batteries are at 70% with a target of 71 at this time of day, thus the charger would be disabled. I ramp up charging current from 8A in 1A increments as long as the SOC is > 3% over the target. I ramp down in 4A increments if SOC falls below the sliding TGT. I sample every 2 minutes. SOC > 95% (my target ceiling) ramps to 32A immediately. My
That is one heck of a system. Is it possible you could technically describe how you put it all together for example how many batteries connected to each inverter and how that was done for load sharing, how are the inverters paralleled together, how is the PV divided up between the units etc

target floor is 20% at 0730. I will bleed off power from the batteries in the early AM , might as well as long as I can get a full charge (to 90% or so) the next day. I got happy and wrote a script, but the openevse has some integrations where you can do similar things with various platforms to control charging. I would not let this be a deterrent. $100K buys a lot of propane and extra battery. 200KWH in 4 full-size RUIXU racks would set you back around $50K. If at 100% it would charge a Tesla from ZERO and run the house for two days with zero sun. Not sure how many people will be scrambling up there in the grayest gloomiest winter with an EV, but with the artificial government push, the number of EV's will be increasing.

Most people with EV's going up to a cabin, even on grid, don't assume they will have access to more than 120/15a, which is pointless with most electric vehicles these days. The other thing would be to put in an L2 pay station, beef up the batteries, and let the genny take up the slack. Supporting an EV is not that complicated. You'll want a security camera in your parking area/gar

Hi @djparnell and welcome to the forum. Well, I can't help you too much right now except for my planning, but feel free to follow my progress over the next year or two. My wife and I are building an off grid barn/garage (36x44) with living quarters over it right now (should be weathertight in July) and then a 40x40 home either late this year or more likely next (contractor availability). We're in midcoast-central Maine and given that our current home just a few miles away just sold quickly, we're going to be living there starting in September, in the barn quarters until the house is built (will be pretty nice barn quarters, so not too much of a hardship). So, we'll be decent test subjects, in a real world situation except that we'll likely be less wasteful than renters (we have a house we rent out on VRBO and renters are often horrible about energy use).

I can say that once you solve the heat problem, off grid appears to be attainable. I have several friends in the area who do it now. We're going with a heat pump (not propane) dryer and electric stove with induction cooktop, and heat pump hot water heater, and even then my math says its perfectly achievable as long as we don't try to heat with electric. Both buildings will have R40 walls, R60 ceilings, triple pane (U-factor 0.18) windows but even then, heat (not AC, as summer brings sun) is the real problem. So, we're installing a propane boiler with hydronic heat, and air source heat pumps for AC and even shoulder season (when the sun cooperates) heat. I see no need for air circulation other than an ERV, which accomplishes that and far more, so I respectfully suggest you rethink heating and consider hydronic, as water is a wonderful heat transfer medium - much more efficient than air.

Where things will get interesting for us is when we also install an air-to-water heat pump, once Mitsubishi releases their new model to the US. We'll then automate the hydronic to switch back and forth between that unit and the propane boiler based on outside air temp (not the biggest factor actually) and sun availability (that's the big factor), as the source of heat for the buffer tank. It may take years to break even on that, but since I gave up golf and avoided a boat I need an expensive hobby :) .

Where I THINK (we're going to find out soon enough!) many people go astray is a feeling that they need many days of battery backup, no matter what happens. If my math is right, we'll have about 4-4.5 days of battery in the building we're occupying as our primary residence (first the barn quarters, then the house) at just 42KWH of battery, with normal energy use, if we don't use electricity (heat pump) for heat. I'll report back on that through the winter. And if I'm wrong, well, we'll just recharge with a few hours use of the generator, which most people seem to forget or think they need to avoid. If I must recharge even once per week in the worst weeks of the year by running the generator for a few hours, I'm fine with that. It becomes a tool for avoiding a grid connection rather than an emergency backup. Might be worth considering that view. Anyway, once we start the install in a few weeks I'll start a thread in Show and Tell and document what happens.
This is great feedback. Thanks! Yes, it will be great to watch your story unfold.
 
I kind of assumed some kind of heat pump/condenser combo would be standard with propane secondary, when I said "no electric heat" I meant resistive heat strips, I should have been more specific.
I would 100% agree with no resistive heat.

I absolutely agree the problem is simultaneous maximum demand which is why I recommended staying away from resistive cooking and hot water heating. A countertop inductive cooktop for light cooking is OK but a full size resistive range with oven not so much.
I use induction. Again though in the overall scheme your oven/range just doesn't use that much electricity unless you are running a bakery or a restaurant or something.

If you are going to have the propane tank sitting there to power the standby generator anyway, then gas appliances make a lot of sense. Here is why: 95%+ of the time the average all electric home doesn't use more than 90A of 240V power (22kW) and well more than 50% of the time it doesn't use more than 12kW. The reason that 200A main panel is there is for that small fraction of time when almost all of the big electrical loads (heat/AC, hot water, dryer, range) are all on at the same time. To equal this you would need 4x 12k inverters in parallel, increasing your upfront system cost, your idle system draw, and system inefficiency. Large resistive loads and batteries don't go together very well because at higher rates of discharge the battery efficiency goes way down and now all of the calculations are out the window.
If instead you go with propane appliances you remove all of these resistive loads from the electrical system entirely and you can now run the entire structure on a 100A electrical panel with ease. The money you save paying the electrician for upfront building and install cost will go a long way towards paying for the more expensive appliances, and the cost of two additional 12k inverters can instead be applied to more battery storage.
Most everything you say here is a 100% valid and should not be ignored for sure. I used to feel mostly this way as well. Actually having now installed and running solar, The rebuttal I have starts with CAPEX vs OPEX. The capital expenditure now eliminates a large chunk of the operation expenditure during the lifetime of the project. The cost of propane/other is non-static and unpredictable. Now one guy on this forum was buying propane at a buck or so a gallon, tough to get an ROI on the capital at that price. OTOH if it shoots up to $5 or more that paridigm no longer holds up.

Inverters are relatively cheap. To your load point three 50A inverters (36KW) would likely handle most everything, including an EV or other silly load like a hot-tub or well pumps or .... alongside any other devices. The batteries are where the money pit is.

I think the "Sparky's" here would validate that the cost of wiring your house with a 200A panel and couple extra circuits for an electric range or water heater or what-have-you is nominal/insignificant. The cost difference of a homelife 200A panel vs a 100A panel is $50. A tad of extra wire, and a few breakers. The cost is to pay the electrician to drive his truck over to your house and provide the licenced labor and inspections running a bunch of #14 and #12 all thru it for outlets and lighting is where the money is.

Now you get to pay another pro, to come out and run the gas lines, and get those inspections (Not to mention you just piped a flammable gas inside your home). From a capital standpoint all-electric is going to be less expensive up front. Frankly I'd run the electric to those locations even if I went with gas. Saving $1000 at that point is penny wise and pound foolish.

Re-discharge and resistive with batteries less efficient. I call FUD. I've gone so far as to charge my EV bleeding power from the PV batteries. Transition losses are consistent, I have 60KWH of batteries.

I have a different philosophy on solar than a lot of people I guess. Most of my customers don't have $100k to drop on the solar system so they are looking for another way.
The best way in my opinion is like my retirement home design, passive solar with minimal energy inputs needed for climate control and DC refrigeration, lighting, and cooling. That house will run year around on 12kW of solar and 60kWh of batteries and very little generator time, but it represents a massive lifestyle change that most people don't want to go through.

To quote the OP: "and the quote is $180-$200K from National Grid". I think we surpassed your $100K mark, and you are arguing against spending $10-15K on a couple of extra inverters on property he wants to rent out. If you just want to set up a cabin in the fringe somewhere for two people your arguments hold merit. Once I put other people in it, I want all or mostly electric. Way less hassle, and likely more cost effective in the long run because of the volitility of the price of your fuel sources. The biggest dependency is how much solar you can get, and the cost envelope is going to be around how much battery/electrical storage you need to keep from running the generator to supplement it when it doesn't produce enough. Thats really the ROI calculation, If you build the system to scale up storage you can easily tweak it up if gas goes thru the roof.

One thing I've noted in the past, and has been mentioned here. Someone renting is not paying attention to consumption, even if paying for it if it's a seasonal rental. Thus they will use the gas or the electric as they see fit while they are there. You just have to plan for it.
 
I installed 96 400W panels on the roof of a purpose designed barn, 4x EG4 18k, 8x PowerPro 14.3kWh batteries. It effectively runs his entire property, 2 barns, 2 wells, 3500sqft house, pool. As far as I know he hasn't paid for electricity since but it was installed last fall, hasn't been through a summer yet.
BUT
He still has his grid tie and his low temp heat, cooking, and hot water are propane.
I don't know how much more large scale things would get for a single property, to be honest. This system would probably handle an EV with ease (he wanted it overdesigned and was willing to pay for it) but I want to see a year's worth of usage patterns before saying for sure. Based on his previous electricity billing and the calculated system output, he could charge an EV a few times a week no problem.

Outstanding! Nice! I'd bet his batteries stay at 100% most of the solar day with that much output. To me I think this really hits the target/mark, and makes my "all-electric" point. If you can make the electricity, you can either dump it, and pay for propane/gas for day to day cooking, and heating needs, or just get electric appliances. The worst load is an electric dryer, or HVAC depending on where you live. That being said you can only do so much laundry... And if the HVAC is primarily for Air conditioning your gonna need electricity for that anyway.

Right up there with @B-Mod on the capacity front.
 
Not sure if you've seen the thread where a pair of 18kpvs went berserk and killed a bunch of appliances when a longer crossover cable was accidentally used for the comms instead of the shorter provided straight cable. Any kind of rodent damage to a straight cable could end up with a similar failure so protect it well.
FUD! Jeeze, not this again. I would find it highly unlikely a rodent chewing thru the cable would create the bizarre signal cross wire condition encountered in that thread because someone used a random RJ-45 cable that was wired to shuffle the pinouts at each end scrambling the sync signals. Further with 4 inverters the cables should be in a full communication loop. If any condition causes a disconnect the inverters shut down they do not go "berzerk". This gentleman seems to be a competent installer, I doubt he would make such a severe wiring error.
 
Outstanding! Nice! I'd bet his batteries stay at 100% most of the solar day with that much output. To me I think this really hits the target/mark, and makes my "all-electric" point. If you can make the electricity, you can either dump it, and pay for propane/gas for day to day cooking, and heating needs, or just get electric appliances. The worst load is an electric dryer, or HVAC depending on where you live. That being said you can only do so much laundry... And if the HVAC is primarily for Air conditioning your gonna need electricity for that anyway.

Right up there with @B-Mod on the capacity front.
He has a little way to go, I am at around 185 or so 400 watt panels, lol.
 
I think the "Sparky's" here would validate that the cost of wiring your house with a 200A panel and couple extra circuits for an electric range or water heater or what-have-you is nominal/insignificant.
I am a "Sparky" have been for almost 25 years. I don't normally play in the residential market because it doesn't pay well but I have wired more than a few houses nonetheless.
Just to throw out an example, the 8/3 romex to feed the 50A range plug is currently around $2.50/ft and is one of the largest single line item expenses after the panel/breakers and the 12/2 romex for all of the normal circuits. 10/3 for the dryer is not exactly cheap either and then there is the labor to run those dedicated circuits, the additional breakers, the larger service wire.... it adds up. The 125A panel may only be a little cheaper but that's just the tip of the iceberg.
The difference in the square foot cost for residential wiring (this is how it is bid) between an all electric home and one with gas appliances is significant and will be $500-$800 less for a normal size house. Electricians that don't adjust their pricing in these instances are not being honest. This will cover most of the difference in appliance cost for gas stove, gas HWH, and gas dryer. You will still need your plumber to run the gas line and that's not an insignificant expense but IMO it beats doubling the size of the solar system.

I agree on not being dependent on a fossil fuel. Personally I don't like these designs where people want to live in a standard construction house with standard appliances and use solar to "replace" the grid tie. (I have refused any projects that attempt to do this with a "manufactured" home.) I would rather see construction designs that are purpose built for efficiency up front (no, I'm not talking about just extra insulation) resulting in a much smaller power need to begin with, and THEN sizing the solar system to match that. I would rather see $50k spent on a more efficient structure than $50k spent on a larger solar system, even if that means my contract is smaller. In these types of houses, you typically don't even have a large inverter (or multiple inverters) that's sitting there knocking nearly 10% efficiency off of the entire system, you are using as much raw DC as possible and only using AC on an as needed basis. Now you are in a place where you can ditch the backup generator and spend that on more battery storage instead, and use a couple of DC high efficiency mini-split heat pump systems for 90% of your heating and cooling with maybe a bit of wood in the winter, solar hot water.... the knowledge and technology is available. Maybe add a couple of vertical wind generators that don't need to be on a tower for some additional resilience on cloudy days (the ROI on this varies by location, obviously).

If I sound like I am on a bit of a crusade, I guess that is true. If I could distill it down to a single statement, it would look like "Most people that want to go off grid need a better architect, not a bigger solar system" at least in most cases. I think that "An ounce of prevention is worth a pound of cure" has never been more true than with an off grid structure. Every kWh of energy you don't use is roughly 1.15-1.25kWh you don't need to produce and store and represents potentially thousands of dollars that don't need to be spent on equipment and the maintenance thereof.

Once there is no propane needed for the backup generator the arguments for putting a propane tank on the property get very weak. However, for most of my customers who have chosen to go off grid this ends up being the solution that their families can live with. They don't want to make any changes to their lifestyle or building plans and they don't want to spend $100k on solar, so that's where it ends up, utilizing a secondary energy source. I would argue this is just spreading that expense over time instead of up front but budget limits win out. It is less than ideal in many respects but in Oklahoma there are gas separation plants everywhere in the midstream natgas chain and propane is relatively abundant and fairly inexpensive if bought in bulk during the lower price times of the year. Mileage on this will vary in other locations I'm sure.
 
Last edited:
FUD! Jeeze, not this again. I would find it highly unlikely a rodent chewing thru the cable would create the bizarre signal cross wire condition encountered in that thread because someone used a random RJ-45 cable that was wired to shuffle the pinouts at each end scrambling the sync signals. Further with 4 inverters the cables should be in a full communication loop. If any condition causes a disconnect the inverters shut down they do not go "berzerk". This gentleman seems to be a competent installer, I doubt he would make such a severe wiring error.
All RJ45 cables should ALWAYS be tested IMO, even "factory" ones. With there being two different standards and those wires being so small and darn hard to see, it is very easy for them to be wrong and I have done it more than a few times myself.
And yes the factory instructions show creating a network loop and there is a very good reason for that, factory instructions are not a suggestion.
 
Last edited:
Most people that want to go off grid need a better architect, not a bigger solar system" at least in most cases. I think that "An ounce of prevention is worth a pound of cure" has never been more true than with an off grid structure.
If everyone was building new perhaps.
Even retrofitting existing structures isn’t cheap.
Easier and cheaper to size the solar plant to make up for any shortcomings in architecture.
 
If everyone was building new perhaps.
Even retrofitting existing structures isn’t cheap.
Easier and cheaper to size the solar plant to make up for any shortcomings in architecture.
Absolutely true, retrofitting is the hardest and most expensive path and sometimes the larger solar system is the best option.
This is unfortunately the bulk of my work with people going off grid. I have to admit it does pose the biggest challenges from the standpoint of the electrical contractor.
Most of my solar installs are still grid tied, however. I am starting to get more interest in combing this with batteries instead of a standby generator, which is a good start IMO.
 
he difference in the square foot cost for residential wiring (this is how it is bid) between an all electric home and one with gas appliances is significant and will be $500-$800 less for a normal size house.
That's a number for sure. Several years ago, I asked a guy to run fiber to a building about 150 ft away. He bid it with copper. I said no, ... fiber. He said "but fiber is going to cost you about $800 more!". At which point I looked at the $4500 quote and said: "So $5300 instead of $4500, how soon can you get started". If I'm spending $200K or so on a house, saving even $1000 to not wire for electric is dumb IMNSHO.

Solar keeps getting better and less expensive, battery capacity is moving faster than the equipment. WTH.

Once there is no propane needed for the backup generator the arguments for putting a propane tank on the property get very weak.
I don't think you can get out from under having some fuel based generation unless you are willing to go dark every once and a while. What we are talking about is where the curves are that minimize costs/roi and how much you need it.

Building efficiently is a no-brainer, but the electric vs gas appliance argument is ROI on capex vs opex. Gas dryers really dry clothes fast, but I find them a little scary. Ditto on a gas HWH, but I do like demand gas heating of water. Sadly this is sub-optimal for a solar build out because of demand. Gas heat used to be drastically less expensive, not so much these days with the improvements in heat pumps. A lot of people really like cooking with gas, I have used both extensively and much prefer electric. In a commercial environment gas is usually drastically cheaper if you can get it piped in, but I really like my induction range, and prefer the temperature control of electric surface units over the heat control of gas ones. Induction is amazing. Running a couple-of-four pizza ovens full blast, gonna have to go with gas, I have had both, recovery time with gas is much better, but that is not a residental use pattern, and the truck is not delivering propane.

We have modern conveniences for a reason. I am 100% capable of living off grid in 'survival' mode with a bowie knife and the clothes on my back for as long as it takes, should the need arise. This could cost me $0. This is not the lifestyle I prefer. As Bill Mahr put it, "If I can fly private, I want to fly private". The question is the monetary pain threshold for your desired lifestyle. In the case of the OP he's looking at a $200K expense to get electricity to his land, which he appears to want to set up and rent out probably as an airbnb, and use himself on occasion until moving there permenantly when he retires. I think $100K could put in a very nice power plant that would exceed his initial need and if properly designed allow scaling up if he adds other dwellings to the property without sacrificing any lifestyle choices, and be all electric.
 
Even retrofitting existing structures isn’t cheap.
My brother owns a construction company in Charleston. There are laws on the books that prevent demolishing some of the structures that are "historical" in nature. Myriad rules on remodeling and maintaining the "integrity" of the existing structure while doing so. Oddly many of these buildings get abandoned, taken over by careless homeless people, catch fire, and burn down. At which point they can be rebuilt with modern materials as long as they maintain the original architectural look.
 
My brother owns a construction company in Charleston. There are laws on the books that prevent demolishing some of the structures that are "historical" in nature. Myriad rules on remodeling and maintaining the "integrity" of the existing structure while doing so. Oddly many of these buildings get abandoned, taken over by careless homeless people, catch fire, and burn down. At which point they can be rebuilt with modern materials as long as they maintain the original architectural look.
Charleston SC is it’s own animal.

Knew a guy who bought a house on the battery and he was telling me about the hundreds of hoops he had to jump through just to paint the place.
 
I am a "Sparky" have been for almost 25 years. I don't normally play in the residential market because it doesn't pay well but I have wired more than a few houses nonetheless.
Just to throw out an example, the 8/3 romex to feed the 50A range plug is currently around $2.50/ft and is one of the largest single line item expenses after the panel/breakers and the 12/2 romex for all of the normal circuits. 10/3 for the dryer is not exactly cheap either and then there is the labor to run those dedicated circuits, the additional breakers, the larger service wire.... it adds up. The 125A panel may only be a little cheaper but that's just the tip of the iceberg.
The difference in the square foot cost for residential wiring (this is how it is bid) between an all electric home and one with gas appliances is significant and will be $500-$800 less for a normal size house. Electricians that don't adjust their pricing in these instances are not being honest. This will cover most of the difference in appliance cost for gas stove, gas HWH, and gas dryer. You will still need your plumber to run the gas line and that's not an insignificant expense but IMO it beats doubling the size of the solar system.

I agree on not being dependent on a fossil fuel. Personally I don't like these designs where people want to live in a standard construction house with standard appliances and use solar to "replace" the grid tie. (I have refused any projects that attempt to do this with a "manufactured" home.) I would rather see construction designs that are purpose built for efficiency up front (no, I'm not talking about just extra insulation) resulting in a much smaller power need to begin with, and THEN sizing the solar system to match that. I would rather see $50k spent on a more efficient structure than $50k spent on a larger solar system, even if that means my contract is smaller. In these types of houses, you typically don't even have a large inverter (or multiple inverters) that's sitting there knocking nearly 10% efficiency off of the entire system, you are using as much raw DC as possible and only using AC on an as needed basis. Now you are in a place where you can ditch the backup generator and spend that on more battery storage instead, and use a couple of DC high efficiency mini-split heat pump systems for 90% of your heating and cooling with maybe a bit of wood in the winter, solar hot water.... the knowledge and technology is available. Maybe add a couple of vertical wind generators that don't need to be on a tower for some additional resilience on cloudy days (the ROI on this varies by location, obviously).

If I sound like I am on a bit of a crusade, I guess that is true. If I could distill it down to a single statement, it would look like "Most people that want to go off grid need a better architect, not a bigger solar system" at least in most cases. I think that "An ounce of prevention is worth a pound of cure" has never been more true than with an off grid structure. Every kWh of energy you don't use is roughly 1.15-1.25kWh you don't need to produce and store and represents potentially thousands of dollars that don't need to be spent on equipment and the maintenance thereof.

Once there is no propane needed for the backup generator the arguments for putting a propane tank on the property get very weak. However, for most of my customers who have chosen to go off grid this ends up being the solution that their families can live with. They don't want to make any changes to their lifestyle or building plans and they don't want to spend $100k on solar, so that's where it ends up, utilizing a secondary energy source. I would argue this is just spreading that expense over time instead of up front but budget limits win out. It is less than ideal in many respects but in Oklahoma there are gas separation plants everywhere in the midstream natgas chain and propane is relatively abundant and fairly inexpensive if bought in bulk during the lower price times of the year. Mileage on this will vary in other locations I'm sure.

Hello Everyone,

My name is David. I live in NY, and have property in the Adirondacks that I am building on this year. I am - and have been for a few years - weighing whether or not I want to make this an off-grid build. So, I am reaching out to, well, anyone that will give me their experience with off-grid living to help me make that decision.

My energy needs were calculated based on my family's current avg. energy usage - ~30KWhs per day - and I worked with two different solar engineers to spec out a system. Of course, we factored peak sun hours per day, as they historically occur in my property's zip code. Using 3 days of autonomy, at the lowest avg. sun hours per day (in December), the system came out as: 13KW PV array and ~2000AH of LifePo batteries. Just to be safe, though, I purchased 26KWs of Longi bifacials, thus doubling the array size. Of course, we would have a backup generator as well.

The build will be ~1200 sq. ft., and built very tight, with spray foam insulation.

Why am I considering and off-grid build? I do not have a pole to my property - the nearest being ~1 mile away - and the quote is $180-$200K from National Grid. I know this is a lot, and I am sure that most-if-not-all that are reading this - on this forum, in particular - are thinking "That's ridiculous. Solar is a no-brainer." That said, please consider the rest of my considerations:

(i) When not in use, I will be renting the property. Renters are not energy conscious.

(ii) I will be adding more, but smaller, builds to the property in the future for rental purposes.

(iii) I do NOT want to be constantly thinking about energy usage / conservation when I am using it.

(iv) I do NOT want to be working on the array/inverters/batteries regularly.

(vi) Based on early quotes, between hardware and installation, the solar will cost ~$80 - $100K. This is before tax credits.

With that in mind, and despite my best searching/reading efforts on line, I have yet to find anyone - and I mean, NO ONE - that has said something along the lines of "Well, we have X-size array and Y-sized battery bank, and we never have to worry about power. We threw in central air, and have a hot tub, and we never worry about whether the batteries are drawing down." There seems to always be some discussion about raising the thermostat in the summer during a cloudy stretch; fear of installing heat pumps; no one uses central air - all mini-splits; etc.

So, with that as my back drop, is there anyone on the forum that has (i) built a 1200 ft. + house (not a small cabin) that supports a family, and (ii) has installed a large solar/PV system with a battery back up in the North East that has had a smooth experience? What do I mean by "smooth"? The system, (a) for all intents and purposes run itself without frequent inspection/intervention, and (b) the backup generator only runs, say, 5 or 10 times per year.

If, for instance, I were able to install a system for the cost that I've spec'd, and it ran "smoothly", then I'd likely go with the Solar, and could scale up accordingly for the other builds. But, if real world experience - at a larger scale - finds that the generator is often running, and there are semi-frequent-to-frequent interventions necessary, then I'd likely bite the bullet.

Please know that I write this with a true spirit of inquisition, humility and curiosity. I'd love to have a great off-grid system. Who wouldn’t? But I am building this property as an asset, and with future plans in mind, so I want to do it right the first time, even if that means bending over backwards to do so.

Thank you in advance to anyone that will afford me their time.
I appreciate everyone's thoughts on this.

I'm going up there to meet a potential installer in a week or two, and their feedback will be helpful in the decisionmaking, too. I will keep you all posted. I truly appreciate the time everyone has given me!
 