Rookie mistake, please help?

I have a 2200w inverter so have bought 4/0 + and - cables to move from inverter to batteries.
The 1 awg that was there heated up under 1000w loads or higher.

But I forgot about the fuse/circuit breaker.
(fuse now, breaker screwed on panel but won't use til ironing this out).

Can I mix 4/0 awg from inverter down to breaker with 1/0 from breaker down to batteries?
Or do I need 4/0 all the way to avoid overheating?
 
Do you have 1awg or 1/0awg? They are different.

Wires are supposed to heat up when used anywhere near their current rating, and current ratings for various wires are based on temperature.

Using larger wires is fine, but you should fuse/breaker for the thinnest wire in the circuit. The shorter wire will have less total resistance, but it may still get warm. Please see the chart in link #2 in my signature. It is the AWG chart, and it shows wire ratings for different temperatures. Note that the lowest listed is 125A @ 60°C. 60°C is effing HOT to the touch. 175A @ 90°C will almost boil water. Marine ratings go to 105°C, which can boil water.

FWIW, 2X 1/0 wires are almost identical to a single 4/0 wire. If you double up the 1/0, you have 4/0 the whole way.
 
I'm installing 4/0 from inverter to fuse/breaker on positive (and negative to battery) and HOPE I can install 1/0 (or 2 lenghts of 1/0 to share load, if I understand you correctly) from fuse/breaker to battery bank.

The battery bank is connected like this:

4/0 positive + in from inverter to fuse
1/0 (or 2 strands of 1/0) from circuit breaker to battery 1

battery 1 has 1awg to battery 2 (on both + & -)
battery 2 has 2awg to battery 3 (on both + & -)
battery 3 has 1awg to battery 4 (on both + & -)

then 4/0 out of bank to inverter negative.

So far so good
 
I have a 250a inline fuse right now, and a 250a tocas breaker screwed in right next to in on the board
(I didn't want to switch over until I sorted out my wiring).
PS: Thanks for the links/wisdom.

Do you have 1awg or 1/0awg? They are different.

Wires are supposed to heat up when used anywhere near their current rating, and current ratings for various wires are based on temperature.

Using larger wires is fine, but you should fuse/breaker for the thinnest wire in the circuit. The shorter wire will have less total resistance, but it may still get warm. Please see the chart in link #2 in my signature. It is the AWG chart, and it shows wire ratings for different temperatures. Note that the lowest listed is 125A @ 60°C. 60°C is effing HOT to the touch. 175A @ 90°C will almost boil water. Marine ratings go to 105°C, which can boil water.

FWIW, 2X 1/0 wires are almost identical to a single 4/0 wire. If you double up the 1/0, you have 4/0 the whole way.
 
As @snoobler said, you can use any wire you want as long as the fuse protects the smallest wire. In your case the smallest wire is 2 AWG. You could put a smaller fuse on that wire but a 250 Amp fuse will not protect 2 AWG wire.
 
The fuse bnetween battery and inverter is where the whires heat up.
What size fuse should I be using bewtween them? Or should I replace the 2 wire with 1?

As @snoobler said, you can use any wire you want as long as the fuse protects the smallest wire. In your case the smallest wire is 2 AWG. You could put a smaller fuse on that wire but a 250 Amp fuse will not protect 2 AWG wire.
 
What size fuse should I be using bewtween them? Or should I replace the 2 wire with 1?
You can replace the wire or you can go to the table mentioned above and use the correct fuse for the existing wire. The choice is yours. If it were me, I would base it on what I had in my spare parts bin and how much load I expected that connection to have.
 
Is moving up to 1 awg on the battery enough for the fuse?
The Max load I will draw is 1500w at any one time.

Thx in advance!
 
What does the chart say? I would have to look that up to answer your question.
1500 Watts is how many Amps at 12 volts?
 
Is moving up to 1 awg on the battery enough for the fuse?
The Max load I will draw is 1500w at any one time.

Thx in advance!

Depends on your system voltage and the round trip circuit length.
If you have a 1500 watt inverter at 12 volts....
1500 ac watts * 1.15 inverter efficiency / 12 volts = 143.75 dc amps
143.75 dc amps * 1.25 fuse headroom = 179.6875 fuse amps
 
Depends on your system voltage and the round trip circuit length.
If you have a 1500 watt inverter at 12 volts....
1500 ac watts * 1.15 inverter efficiency / 12 volts = 143.75 dc amps
143.75 dc amps * 1.25 fuse headroom = 179.6875 fuse amps
Just a question, if he has 144 amps to account for, why are the wires heating up with using 1/0 wire when the calculator shows wire as small as #4 ? I understand that there is energy loss but I have #2 wires that regularly pull 1000 to 1500 watts from my inverter and they stay pretty cool. Now if they start pulling 2500 watts they do start heating up. Of course my wires are only 2 foot long.
 
Just a question, if he has 144 amps to account for, why are the wires heating up with using 1/0 wire when the calculator shows wire as small as #4 ? I understand that there is energy loss but I have #2 wires that regularly pull 1000 to 1500 watts from my inverter and they stay pretty cool. Now if they start pulling 2500 watts they do start heating up. Of course my wires are only 2 foot long.
Ok, I may have figured it out, I am running 24 volts not 12. DUH
 
Just a question, if he has 144 amps to account for, why are the wires heating up with using 1/0 wire when the calculator shows wire as small as #4 ? I understand that there is energy loss but I have #2 wires that regularly pull 1000 to 1500 watts from my inverter and they stay pretty cool. Now if they start pulling 2500 watts they do start heating up. Of course my wires are only 2 foot long.
how hot are the wires actually getting?
 
Ok I get it, since mine is 24 volt at 1500 watts that would be a little over 63 amps for me.
1500 watts @ 24 volts ...
1500 * 1.15 / 24 = 71.875 dc amps
71.875 * 1.25 = 89.834375 fuse amps
Ohhhh the lights are getting dim. ?
 
1500 watts @ 24 volts ...
1500 * 1.15 / 24 = 71.875 dc amps
71.875 * 1.25 = 89.834375 fuse amps
Ohhhh the lights are getting dim. ?
I am just learning and asking questions. That is why I do not understand the Bos'ns calculator. Even at 89 amps it still shows wire at #6 is ok?
 