Ok perfect I would do everything and show you when I finish thank you so so much you have been my guardian angel thanks really
I put everything as you say and send you photos thanks you so much u have been my guardian angel hehehe a big thanks really. A question can I switch the green and the white I just ask so I don’t need to cut off the o-ring adapter that I put on the white cable at the inverter Ac outputAt the panel. Keep all colors the same.
White and green must go to the neutral/ground bar.
Black goes to ONE leg of the main breaker.
at the inverter
Put the black wire on L
Put the white wire on the N
Put the green wire on the G earth terminal.
do the same for the ac output.
now...
We need to see how you have the plugs and outlets wired, because that ALSO must match.
At the panel. Keep all colors the same.
White and green must go to the neutral/ground bar.
Black goes to ONE leg of the main breaker.
at the inverter
Put the black wire on L
Put the white wire on the N
Put the green wire on the G earth terminal.
do the same for the ac output.
now...
We need to see how you have the plugs and outlets wired, because that ALSO must match.
Yes.View attachment 38175
like this
Everything work great you are a genius thank you so so so so much you know the funny part of this that I’m an idiot and I pay for an electrician to put the Ac input outlet the one that is on the main grid outside and I pay for a bad work so he just see my stupid face and do a shit of work and told me everything was great. But anyways everything it’s fix know thanks so much.The plastic nut is fine.
This outlet needs to be rain tight, or it will corrode and fail in short order.View attachment 38135
Everything in blue it’s the connection of the Ac input everything in red is the Ac output and everything in green are the grounds as u can see they are 5 ground in the same connection the Ac input, Ac output, house ground, the meter, and the ground going to the ground literally
Yes that the saddest part that I pay for that and I almost blow beyond the atmosphere ??YOU ARE KIDDING!
An ELECTRICIAN did that? Wow. That is horrible.
as for charging, what is the display saying?
Yes, for the outside outlets.That would be for the outlet in the outside?
that’s a better idea that the one I have I was thinking of buying a plastic box like this one so i can put the outlet insideView attachment 38204
If this is the work they do, DO NOT CALL THEM BACK!Yes that the saddest part that I pay for that and I almost blow beyond the atmosphere ??
Don’t say nothings the display I just saying that it’s taking power from the batteries until a few minutes ago that change to get power from the main because I program it to do that but I don’t know why the batteries don’t charge I think it’s some programming problem to so I would need to read all the programming and check what’s is wrong with.
but yea a freaking electrician do this freaking horrendous job a few days ago and I been calling him and he’s always saying tomorrow I would go tomorrow but that’s another problem I would fix in this days with that horrendous electrician