380w x 6 panels is 2280wI have 6 of these panels in 2S3P...the 2S are putting out about 95v and over 20A...I was expecting a bit less.
Can someone explain this to me...I am confused. Is the bifacial producing at that efficiency?
Thanks in advance.
Cheers,
Mike
View attachment 42969View attachment 42970View attachment 42971
24V battery
I am getting over 60amps...over 20 per string
Yeah thinking in Amps without Voltage will confuse.Are you getting more watts than your panels' rating? What? Power (watts) equals volts times amps. Only thing that really matters is watts, or watt hours, collected by your panels.
The MPPT does it's thing ... doesn't matter how.
Not more watts...more amps than I expected and had designed the system for...I was assuming I would get about 10-15 amps from each string of 2 panels with three strings in parallel keeping it below 45amps...I completely misunderstood.Are you getting more watts than your panels' rating? What? Power (watts) equals volts times amps. Only thing that really matters is watts, or watt hours, collected by your panels.
The MPPT does it's thing ... doesn't matter how.
What design?Not more watts...more amps than I expected and had designed the system for...I was assuming I would get about 10-15 amps from each string of 2 panels with three strings in parallel keeping it below 45amps...I completely misunderstood.
Yeah thinking in Amps without Voltage will confuse.
His 380w x 6 panels is 2280w
His readout says 1710w input.
That's 75% which is pretty
When I take a multimeter and plug it directly into the panels I am getting the larger than expected amps...that does matter and is to be expected? ....I measure two panels in series at the panels and get ~90volts and ~23amps about the same measurement 125' away at the electric panel. 6AWG ....I just don't understand the 23amps...that would be over 2kw at 90 volts for 2 380 watt panels?? Am I still confused. Yep.You're still not getting it. The Amps that come out of the panels is not directly related to the Amps that go into your battery. Think of the MPPT as a variable transformer. It takes the voltage and current from your panels and "transforms" them to the proper values for your battery bank. (As the panels and the batteries determine.)
When I take a multimeter and plug it directly into the panels I am getting the larger than expected amps...that does matter and is to be expected? ....I measure two panels in series at the panels and get ~90volts and ~23amps about the same measurement 125' away at the electric panel. 6AWG ....I just don't understand the 23amps...that would be over 2kw at 90 volts for 380 watt panel?? Am I still confused. Yep.
Thanks for your patience...
I tested across the leads in full sun like I did with voltage changing the setting on my meter to DC Amps...at the combiner box with all panels I get up to 70amps...I am likely doing something wrong?...I get the same readings from the GrowattThis is what happens with MPPT:
PV volts * PV Amps = Battery Volts * Battery Amps.
Panel input power = battery charge power
Are you saying that you took only two panels in series, and shorted their (+) to (-) leads together and measured 23A?