Generator Output Amps.. Is this as expected?

Old_Skewler

Solar Enthusiast
Joined
Jul 30, 2021
Messages
510
Location
NYS
Got a clamp meter and went happily to measure the output current out of my 240V generator and this is what I got:

- RED: 11.77A
- BLACK: 11.87A
- WHITE: 6.86A

Is this as expected? I just don't understand why the neutral line would 6.86A and not 22A.

Could someone please explain me the science behind these numbers?

Thanks in advance!

20230702_113447.jpg20230702_113455.jpg20230702_113504.jpg
 
In a split-phase system. The neutral only carries the unbalanced load. Whatever is on L1 and L2 are canceled out by each other. And the remainder is returned on the neutral.

- RED: 11.77A
- BLACK: 11.87A
- WHITE: 6.86A
Although this math doesn't seem right.
I would expect only 0.10a on the neutral. (Approximately)
 
Either way I wouldn't worry about it as long as everything works.
 
Because you have 120v items running
So if I isolated the cabin, which is wired in split-phase, and only ran the inverter charger (240V) then i should see a reduced Neutral leg delta?

I'lll try it.

Thanks!
 
No load, static load (restive), different load (W) on each leg?
 
Got a clamp meter and went happily to measure the output current out of my 240V generator and this is what I got:

- RED: 11.77A
- BLACK: 11.87A
- WHITE: 6.86A

Is this as expected? I just don't understand why the neutral line would 6.86A and not 22A.

Could someone please explain me the science behind these numbers?

Thanks in advance!

View attachment 155920View attachment 155921View attachment 155922
If 3 phase is an option. https://calculator.academy/neutral-current-calculator/ A 11.87, B 11.77, C 9.202 = 6.86 neutral
 