AC Output connections from 6000xp to sub panel

I am measuring voltage between ground and neutral, and ground an black (open circuit) that were entering my old Growatt inverter before being connected to the inverter.
I think you mean between white and ground, which would be L2 and ground...
You were using ground for neutral.
 
The input to the Growatt is a 240v line (black and white) and a ground. The output is the same that I have been using for my sub panel.
That cable doesn't have a neutral.
It only has
Black = L1
White = L2
Bare = ground
 
I think you mean between white and ground, which would be L2 and ground...
You were using ground for neutral.

I think you mean between white and ground, which would be L2 and ground...
You were using ground for neutral.
I am thinking of black and white as L1 and L2. And the potential of each of these to ground (the bare copper wire) is 120v giveing the total 240 v between L1 and L2.
 
I am thinking of black and white as L1 and L2. And the potential of each of these to ground (the bare copper wire) is 120v giveing the total 240 v between L1 and L2.
In this case, you are not running a ground, you are running a neutral.
You STILL need a ground.
 
I am familiar with that unit.
It's input is 240v 3-wire single phase.
Two hots and a ground.
No neutral.
 
Yes, that is my conclusion too. Red, Black, Neutral and ground. Do you agree with the connections to my sub panel given above, which was my orginal question.
 