I wouldn't have used bare copper. But it's fine if you can make sure that it's not in contact with the aluminum frames anywhere. (Galvanic corrosion from dissimilar metal contact)
Disconnect it from the local auxiliary ground rod, to protect your equipment and appliances from the gradient pulse created by a nearby lighting strike. Unless you live somewhere that never has lighting.
But even then, I still wouldn't recommend it.
It has no purpose. And only provides a false sense of security.
This should also be 0v.
But maybe the Sol-Ark isn't completely isolating the PV. (That would surprise me)
This doesn't make sense with the above. (Contradictory)
The ground bar in the Sol-Ark connections areas.
Sorry, this was a typo:
"All panels frames PV+ and frame = 0 volts
This doesn't make sense with the above. (Contradictory)+
The Sol-Ark 15K is throwing an immediate F23 error : TZ_GFCI_OC Fault when the PV switch is turned from off to on.
Testing of arrays completed so far:
Each individual panel was visually inspected for damage. Each individual panels was tested for power output, Voc, Vmpp ,Imp, with a solar multimeter. Each panel had voltage measured by connection to panel frame and then to panel MC4+ and MC4 - PV outputs. all voltages read zero. All panels had newly installed MC4 connectors and conductivity verified.
The serial string terminates in a Midnite Solar MNPV6. The PV+ and PV- go into a Midnite Solar 15 amp 600 VDC breaker DIN mounted to the combiner box. The output from this breaker goes into a 20 amp little fuse, DIN mounted, both the PV + and - negative are fused.
The PV - goes to an isolated buss bar where there is the connection to the DC ON/OFF switch made by Schneider. The PV+ from the fuse goes directly to the DC ON/OFF switch. The grounding of the array is as follows: 10 foot grounding rod with bare copper wire is attached to the frame of each panel by an approved grounding lug. Each end of the bare grounding wire terminates on the buss bar of the MNPV6 combiner box. Then a wire from the ground buss travels to the ground buss of the inverter.
Observed voltages: Between PV + and PV- is the expected Voc. Between PV- and ground buss is zero volts. Between PV+ and ground is the Voc voltage. Between PV+ and the metal frame of the array or any part of the combiner box is the same Voc voltage. This the same for all three arrays and I cannot figure out why the PV+ to ground has a measured voltage or where this connection is coming from is there is a jump between the PV- and the ground.
Any ideas?