Hey all, I have an EG4 6500 feeding a critical loads sub panel right now. I have the hot and neutral wires feeding the panel, the hot goes to a single pole of a 70A double pole breaker, the other pole is not connected. The neutral wire is connected to the neutral bar in the panel. Since this a sub panel the neutral and ground bars aren't bonded.
I have not done any upgrades to the firmware on the 6500 since I got the inverter in October '22, and have not removed the N/G bonding screw in the inverter. Because of this, when I transferred the 120V loads to this sub panel from the house panel, I transferred both the hots and neutrals. I did this because the early iterations of the firmware did not create a common neutral.
I am considering upgrading to the 6000XP, which from what I understand, has a common neutral. Is this correct ? Because of this do I need to remove the neutral wires between the main panel and sub panel, and just run the hots? And maybe use a larger wire to connect neutral bars in the main panel and sub panel? Or does it matter?
I should note that this main panel is inside the house but is not bonded N to G as the service panel is outside on the pole and that is bonded.
Thanks
I have not done any upgrades to the firmware on the 6500 since I got the inverter in October '22, and have not removed the N/G bonding screw in the inverter. Because of this, when I transferred the 120V loads to this sub panel from the house panel, I transferred both the hots and neutrals. I did this because the early iterations of the firmware did not create a common neutral.
I am considering upgrading to the 6000XP, which from what I understand, has a common neutral. Is this correct ? Because of this do I need to remove the neutral wires between the main panel and sub panel, and just run the hots? And maybe use a larger wire to connect neutral bars in the main panel and sub panel? Or does it matter?
I should note that this main panel is inside the house but is not bonded N to G as the service panel is outside on the pole and that is bonded.