I just installed a new Must 6000W split phase, pure sign wave inverter. It seems to be working great, but I have noticed that the load percentage seems to be off. It gives a load percentage like to is set for a maximum of 3000W.
Today I finally put a heavy load on the inverter: about 3400 watts. It immediately went into overload falt and showed a load percentage of 110%. Any ideas on why it is showing 110% at only half capacity?
Update:
Ok, problem solved. I found out that the load percentage is the higher of the two phases. The inverter is rated at 3000w per phase, for a total of 6000w.
My old dryer was using 5600 watts!! That is 2800 per line/phase. I had some other stuff running as well, so the highest of the two phases was putting out 3400w or about 110%.
I have a lot to learn, but the inverter is working as it should.
Today I finally put a heavy load on the inverter: about 3400 watts. It immediately went into overload falt and showed a load percentage of 110%. Any ideas on why it is showing 110% at only half capacity?
Update:
Ok, problem solved. I found out that the load percentage is the higher of the two phases. The inverter is rated at 3000w per phase, for a total of 6000w.
My old dryer was using 5600 watts!! That is 2800 per line/phase. I had some other stuff running as well, so the highest of the two phases was putting out 3400w or about 110%.
I have a lot to learn, but the inverter is working as it should.