Growatt 24v 8s 100 ah fortune batteries settings

This is how I built my 24V compression fixture https://diysolarforum.com/posts/245041/

I'm working now on designing two 12V packs for my fishing boat deep cycle batteries. I'll most likely build something similar but add a hinged cover, maybe some sides with perforation. I measured it up today and have plenty of room for 280Ah cells.
 
So the aHr capacity of the battery is not part of the equation and the voltage max of the Growatt determines the size of the PV array but what determines the size of the bms? Is it the max charging current of the Growatt? I will contact Overkill but would like to understand how this works.
 
I would love to know what you find out. I think the max AC charging of a Growatt 24v is 80A. The max solar charging current is 100A. https://www.growatt.com/upload/file/contents/2019/07/5d2eee093f00b.pdf
This is the reply I got from overkill:
The 8s 100a BMS will allow you to discharge at 100a continuously, about 2400 watts.
With 1 battery your inverter will be limited to this power level.
If you added a second complete battery you will be able to fully load the inverter
The specs in my request were for a 310ah 8s battery and Growatt 3000. So this bms will work but will not meet capacity discharge of the Growatt so I'm thinking a 120ah bms would get closer to "fully loading" the Growatt ie. 2880 watts. That make sense?
 
This is the reply I got from overkill:

The specs in my request were for a 310ah 8s battery and Growatt 3000. So this bms will work but will not meet capacity discharge of the Growatt so I'm thinking a 120ah bms would get closer to "fully loading" the Growatt ie. 2880 watts. That make sense?
Overkill BMS doesn't have a 120a BMS in 8S.

You get 2 choices really, add another 8S battery which gives you 200a total or 4800 watts or have a 12V system with two 12V 4S BMS which just gets you to 2880 watts.

I'd prefer the second 8S battery myself. This allows full capacity of a 3000w inverter with plenty of headspace.
 
Overkill BMS doesn't have a 120a BMS in 8S.

You get 2 choices really, add another 8S battery which gives you 200a total or 4800 watts or have a 12V system with two 12V 4S BMS which just gets you to 2880 watts.

I'd prefer the second 8S battery myself. This allows full capacity of a 3000w inverter with plenty of headspace.
Yes, I was looking at the 4s module. Of course I could find a different brand at 120a but prefer the overkill. Just want to make sure what I buy will work.
 
Thanks Zwy!! That’s how i configured mine. Two sets of 100a BMSs, but mine is two 24v setups then paralleled. 8s 200ah. Or 400ah at 24v.

Now if I can just figure out what I want to do for solar panels, and how my local county officials will respond if and when they find them on my house. I just really only want a couple of panels. My setup is more for emergency and fun, but might as well take advantage of the inverter and batteries.
 
Yes, I was looking at the 4s module. Of course I could find a different brand at 120a but prefer the overkill. Just want to make sure what I buy will work.
The problem with running max amps thru any electrical device is the possibility of shortened lifespan. Not saying the Overkill couldn't handle it with no problems but we all know that maxing out anything electrical is more prone to failure.

Of course if the 2880w inverter is way oversized for the load on it, then you're fine.
 