I have an APC SRT3000RMXLA which is a 2u, 2.7kw double conversion UPS

Instead of buying more SLA batteries. Could I replace them with Lithium to get longer lifetime?

The stock configuration is 8 x 12v 5ah SLA batteries, connected to make a 96v pack. Is there a drop in replacements for a 5ah battery, or would it all need to be completely DIY?
 
I do not think so.
Here is the manual for the UPS: https://download.schneider-electric.com/files?p_File_Name=SU_OM_990_5269D_EN.pdf
It seems this is made for lead acid only (Li-ion/NMC and LiFePO4 has different charging characteristics like needs CC-CV charger).

But you can buy a cheap MPP Solar inverter that has the double conversion UPS function too and can give 3-5kW power
for US split phase: https://www.mppsolar.com/v3/lv-mk/ (120V or 2 inverter split phase 240V)
for other: https://www.mppsolar.com/v3/pip-mk-series/ (220-230V 50-60Hz)

And it uses only 48V battery (lead, AGM or any lithium), not 96V (less dangerous).
 
I would think the internal charger of the APC is designed for SLA. Not quite optimal for lithium
 
Thanks guys, that's a shame. Oh well!

For this usage, I think it might be a little overkill to move up to an MPP, the cost of this unit with everything included looks to be about the same as just one of those MPP's
 
Thanks guys, that's a shame. Oh well!

For this usage, I think it might be a little overkill to move up to an MPP, the cost of this unit with everything included looks to be about the same as just one of those MPP's

Just checked. The price of this APC UPS is more than $2500.
A (non US) 5kW MPP MK unit price is ca $720.
If you run servers or a crypto mine ... this inverter even has an MPPT so you can connect up to 4kW solar panels to it.
Even in a big blackout ... you have the power. ?
 
New prices of IT hardware is pretty moot, I got mine for $720 with new batteries

The draw to things like these are also the APC Network cards, I have all my systems setup to shut down if the battery will run out, which is really nice. HOPEFULLY I never lose power again, I bought a portable generator and have a standby generator that will be installed at some point

Solar battery one day
 
The charge profile of the APC ups can be changed via the serial port. There are some guides on the inter webs.
 
I have an APC SRT3000RMXLA which is a 2u, 2.7kw double conversion UPS

Instead of buying more SLA batteries. Could I replace them with Lithium to get longer lifetime?

The stock configuration is 8 x 12v 5ah SLA batteries, connected to make a 96v pack. Is there a drop in replacements for a 5ah battery, or would it all need to be completely DIY?
Hi @IreallyLikeHam ,
Thats a great question.
over the past year, I have specialized in making Lifepo4 replacements for UPS.
The one cavet is, you need High discharge LFP, 26650 cells, S4P2.
To discharge 500 watts from that configuration, 12.8v you need Aprox 40Amp discharge from the pack continuous. it will be 10C continuous discharge from each cell. That is very difficult to source.
I use A123 26650B cells. Second life.
Ups float is 3.45v per cell. it should give me 2-3000 cycles or 5 years of life for the battery pack.

I have made 12,24,36 & 48v battery packs for ups using this method. > 20 packs for family and friends and no issues yet.

Now Im entering Car starting Batteries with same cells. Going great, have 4 cars running, with 0 issues.

Hope my journey will help some out there, same as others stories helped me when I was a Newbie.

Regards
NB
 

Attachments

  • A5007050-B39F-426A-B472-BCCD2B87A944.jpeg
    A5007050-B39F-426A-B472-BCCD2B87A944.jpeg
    156 KB · Views: 25
  • FD32CA51-3C88-466C-9FA5-AA60A32283C2.jpeg
    FD32CA51-3C88-466C-9FA5-AA60A32283C2.jpeg
    137.6 KB · Views: 26
  • 274AE976-8ADA-4840-8DE3-61C80EED33A5.jpeg
    274AE976-8ADA-4840-8DE3-61C80EED33A5.jpeg
    248.8 KB · Views: 25
Hi @IreallyLikeHam ,
Thats a great question.
over the past year, I have specialized in making Lifepo4 replacements for UPS.
The one cavet is, you need High discharge LFP, 26650 cells, S4P2.
To discharge 500 watts from that configuration, 12.8v you need Aprox 40Amp discharge from the pack continuous. it will be 10C continuous discharge from each cell. That is very difficult to source.
I use A123 26650B cells. Second life.
Ups float is 3.45v per cell. it should give me 2-3000 cycles or 5 years of life for the battery pack.

I have made 12,24,36 & 48v battery packs for ups using this method. > 20 packs for family and friends and no issues yet.

Now Im entering Car starting Batteries with same cells. Going great, have 4 cars running, with 0 issues.

Hope my journey will help some out there, same as others stories helped me when I was a Newbie.

Regards
NB
He needs 96v
Most 12v bms cannot series that high a voltage...
 
He needs 96v
Most 12v bms cannot series that high a voltage...
Hi @Supervstech
I dont use BMS on Lifepo4.
The UPS does the max and min Limiting.
Just have to parallel each Cell, then each pack before stringing them in series to make sure they match the voltages.

This, plus Using High Quality A123 B series Cells you eliminate the risk trying to mitigate using a BMS.

Ref:: Do it yourself Lithium Batteries. By Micah Toll.

I have overcharged testing these cells and they pop at >4.6volts, by releasing their vent valve. No fire, explosion, smoke. Just sound and liquid electrolyte smell.
 
Hi @Supervstech
I dont use BMS on Lifepo4.
The UPS does the max and min Limiting.
Just have to parallel each Cell, then each pack before stringing them in series to make sure they match the voltages.

This, plus Using High Quality A123 B series Cells you eliminate the risk trying to mitigate using a BMS.

Ref:: Do it yourself Lithium Batteries. By Micah Toll.

I have overcharged testing these cells and they pop at >4.6volts, by releasing their vent valve. No fire, explosion, smoke. Just sound and liquid electrolyte smell.
Well... that is another option...

Not a recommended option... to each their own. Lfp will wander a lot in series... and without a bms, 4V isn't the max a cell could hit...
 
Well... that is another option...

Not a recommended option... to each their own. Lfp will wander a lot in series... and without a bms, 4V isn't the max a cell could hit...
Yeah, well. I do understand that in this forum, the BMS is considered a hard necessity.
I also understand that because you’re using Large Amp. >50ah ,prismatic cells, volt drifting during discharge an extremely long discharge >1hr , can cause a voltage drift on a extremly flat discharge curve like lfp has. Sometimes even Bell shaped.

Also taking into account Prismatics are not as safe as cylindricals design wise. The jelly band design has its limitations. and 26650 only have 2.2 -2.5 Ah capacity.
The risk balance changes completely from my point of view.

These ups packs usually are very low Ah, since we are looking for <20 mins Runtime until the generator kicks on.

BMS will add >50% to the cost of the pack.

Please challenge my views, that is why we are here at the end. Thinker and Learn.
Rgds
 
Yeah, well. I do understand that in this forum, the BMS is considered a hard necessity.
I also understand that because you’re using Large Amp. >50ah ,prismatic cells, volt drifting during discharge an extremely long discharge >1hr , can cause a voltage drift on a extremly flat discharge curve like lfp has. Sometimes even Bell shaped.

Also taking into account Prismatics are not as safe as cylindricals design wise. The jelly band design has its limitations. and 26650 only have 2.2 -2.5 Ah capacity.
The risk balance changes completely from my point of view.

These ups packs usually are very low Ah, since we are looking for <20 mins Runtime until the generator kicks on.

BMS will add >50% to the cost of the pack.

Please challenge my views, that is why we are here at the end. Thinker and Learn.
Rgds
I tinker... and I have several packs of 32650 lfp cells arranged in 24v packs.
Voltage drifts significantly. I have opened up the packs to find two sets at zero, with sets over 8V... still reaching 24V no venting, still happily operating... obviously the banks will fail rapidly to produce rated capacity this way...
Imagine this drift across 32 or 64 sets? Yikes!
 
I tinker... and I have several packs of 32650 lfp cells arranged in 24v packs.
Voltage drifts significantly. I have opened up the packs to find two sets at zero, with sets over 8V... still reaching 24V no venting, still happily operating... obviously the banks will fail rapidly to produce rated capacity this way...
Imagine this drift across 32 or 64 sets? Yikes!
Yes, Quality cells are of outmost importance.

Do you know the brand of your cells?
Bought them in Alibaba or US?

If what your mentioning is true, there were some serious problems with your build other than voltage drift. I haven’t seen a 3.2v lfp cell @ 8v with electrolyte still inside it.
 
Last edited:
Old military packs. Junk.
Yes LFP has advanced tremendously in the past few years. Its a shame A123 went belly up so many years ago, and sold to chinese conglomerate.
My Second life A123 cells were made in USA that many years ago, but used for server backup. Still 80% capacity.

Start small with a 12v UPS and let me know how it goes. Youll be surprised..!
 

Attachments

  • 81FFBABC-BA66-4715-BFA7-8C8B5E340807.jpeg
    81FFBABC-BA66-4715-BFA7-8C8B5E340807.jpeg
    163.9 KB · Views: 13
  • 572B01E1-BE38-4DB7-B331-04BE87837D22.jpeg
    572B01E1-BE38-4DB7-B331-04BE87837D22.jpeg
    83.2 KB · Views: 13
Last edited:
Any thoughts on connecting one of the 24V 'EG4' battery units to my APC 1400XL as an external battery? Assuming I would need to use the COM port to change the charging profile, but I sure would like a simple rack mount solution for my UPS battery that only lasts 45 min...
 
Any thoughts on connecting one of the 24V 'EG4' battery units to my APC 1400XL as an external battery? Assuming I would need to use the COM port to change the charging profile, but I sure would like a simple rack mount solution for my UPS battery that only lasts 45 min...
Hi @mjcother
If the volts are the same for the LFP battery and the UPS, then its compatible.
Then you have to check the charging profile of the ups, to make sure they are in range of LFP.

min 2.5 v
max 3.64 volts
24v would be 8 series.


The other limitation is if the UPS was designed for long term operations.
Which the one you mentioned seems to be.

Hope this helps
NB
 