I have installed an off grid solar setup in my van. Everything works very nicely until I run any device 1200w+ on the inverter. This causes a 300amp circuit breaker between the battery bank and the 2000w inverter to trip.
I have tried removing everything else from the system entirely so that it is simply the battery bank (4 x 6v flooded in series parrallel) and the inverter (Victron Phoenix Inverter Smart 12/2000).
I have checked all of the cables and they appear cleanly crimped and connected at the terminals.
I have a 1000w heater that can run for a long period without tripping the circuit breaker, but if I add another 200w it will trip. Or if I run my 2000w water heater it trips after about 30-60 seconds.
I've tried 2 300 amp circuit breakers and a 300 amp fuse but all have tripped.
Any help is greatly appreciated as I don't know what else to try. I thought the 2000w water heater would only be drawing 160ish amps at 12v.