any recommendations which firmware is the stable one to use?
I'm kind of surprised you unpackaged it, I would've been tempted to put the new inverter up FS after your previous experience!
 
any recommendations which firmware is the stable one to use?
I've updated to the latest (1.03.11 and 1.04.09) and apart from the initial glitch requiring a change in power locale - all has been good. It's been feeding data to the solarman console (pro.solarmanpv.com) reliably for about ten days.

One thing I did notice, however, is when I added a second string to the unit (I'm in an urban, flat roof environment) the unit rebooted after about a minute, but then recovered nicely.

My config is a 120Ah LifePO4 battery, grid-tied, Load1 fed into a transfer panel and Load2 on an isolated panel and 11x 340W Hanwha Q-Cell Duo panels across two strings (6 and 5). I'm on the grid, but don't feed back into it (Anti-Reverse is enabled).
 

Attachments

  • IMG_3744.jpg
    IMG_3744.jpg
    119.7 KB · Views: 23
  • 6B921C99-CA5A-4FE2-A165-94672332843C.JPG
    6B921C99-CA5A-4FE2-A165-94672332843C.JPG
    258.5 KB · Views: 22
  • 9FFA0907-B654-4D4A-98C8-088EC084348B.JPG
    9FFA0907-B654-4D4A-98C8-088EC084348B.JPG
    504.8 KB · Views: 23
Mine shut down right at dawn as before for the 5 minutes. I also have not had the data stream shut down, yet. knock on wood. That and maybe a bit better synce with the grid are the only things I have noticed improved.

The battery issue seemed to resolve after about 20 minutes.

I happened to be in the basement around 5:30am this morning and I noticed that the unit rebooted about six times in a row for the testing. The power didn't go out to any of the panels (or if it did, it was very quick).
 
I happened to be in the basement around 5:30am this morning and I noticed that the unit rebooted about six times in a row for the testing. The power didn't go out to any of the panels (or if it did, it was very quick).
I now have 2 of the 4 mppt strings hooked up , each with a DC disconnect.
When I disconnect a string, nothing happens except loss of power of the string.
When I re-connect it however, it always needs to start over, not a cold start but a new find of the max power.
From what I understand, each mppt is converted to some "DC middle bus" and from there the AC is generated.
If that bus has a sudden increase of available power, it seems to need to "think about it".
Could it be that at 5:30am it was just enabling a new string ?
I am always amazed by the startup graphs.:
Screenshot from 2022-07-01 12-29-41.png
There is a high voltage very early but it only starts producing amps when there is enough solar.
I live in a valley and both at the beginning and at the end of the day I have a lot of shading going on.
 
Here is the shot of mine. What I see is in the morning when the array voltage reaches 80+ volts it goes into the test. Looks like I get a voltage spike of 150-180 volts on the test. Then back to 85 volts. I do have the isolation test turned on.

1656706943497.png
 
@jsmetalcraft - now that you mention a morning spike, I see the same in mine, right around 5:30 when the voltage starts to pick up. @fromport - I noticed the same thing when adding a string - a soft reboot. I have a 4:2 PV combiner box outside and can flip the strings off and on if necessary.

I also need to get a bigger battery (my 280 Ah is at the cottage), you can see the unit cutting out the PV feed when the battery is full. Since I don't currently feed to the grid, the extra power has nowhere to go.

SOLARMAN_Business-3.png
 
Good morning, I am testing the inverter off-grid with one string solar panels and one lithium battery connected via CAN. For some reason, the inverter only charges using the solar panels for around 30 minutes and then stops giving error "bus over vol". If I do full restart of the inverter, it charges again for around 30 minutes before stopping again. I have firmware version ARM V1.03.11 and DSP V1.04.09. Anyone an idea what could be causing this?
 

Attachments

  • 1.jpg
    1.jpg
    44.6 KB · Views: 5
  • 2.jpg
    2.jpg
    65.8 KB · Views: 5
Good morning, I am testing the inverter off-grid with one string solar panels and one lithium battery connected via CAN. For some reason, the inverter only charges using the solar panels for around 30 minutes and then stops giving error "bus over vol". If I do full restart of the inverter, it charges again for around 30 minutes before stopping again. I have firmware version ARM V1.03.11 and DSP V1.04.09. Anyone an idea what could be causing this?
How many watts total is the array?
In 1. Setup>2. Grid STD>1. React Mode>What is your setting?
How many amps are you charging with?

Reason I ask is I have reported the issue with Bus over VOL and Bat over Vol. Been testing and I used Power Factor instead of React Power yesterday. Ran one day smooth as butter. Knock on wood.

As far as charging I had seen similar but only spikes where the charge would quit but picked right back up without any Warnings. I am about 400 watts over paneled on each three arrays. I covered a few cells on each array and seem to help. I also found that with V1.04.09 I can only get about 70 amps before I have drop outs. Before the update I had gone as high as 140 amps without issue. Ran 100-125 for months, again without issues.

Curious to see if we can narrow down some of these issues and understand some of the setting more fully.
 
How many watts total is the array?
In 1. Setup>2. Grid STD>1. React Mode>What is your setting?
How many amps are you charging with?

Reason I ask is I have reported the issue with Bus over VOL and Bat over Vol. Been testing and I used Power Factor instead of React Power yesterday. Ran one day smooth as butter. Knock on wood.

As far as charging I had seen similar but only spikes where the charge would quit but picked right back up without any Warnings. I am about 400 watts over paneled on each three arrays. I covered a few cells on each array and seem to help. I also found that with V1.04.09 I can only get about 70 amps before I have drop outs. Before the update I had gone as high as 140 amps without issue. Ran 100-125 for months, again without issues.

Curious to see if we can narrow down some of these issues and understand some of the setting more fully.
The array power is only 2.2kW. So max charging would be 40A.
Our setting in
-> Grid STD> US-CA
-> Run Setting> React Mode> React PF> C0.100 (factory setting)
-> Run Setting> React Mode> React RP> 0 (factory setting)
Not sure how to use Power Factor instead React Power?
 
The array power is only 2.2kW. So max charging would be 40A.
Our setting in
-> Grid STD> US-CA
-> Run Setting> React Mode> React PF> C0.100 (factory setting)
-> Run Setting> React Mode> React RP> 0 (factory setting)
Not sure how to use Power Factor instead React Power?
I chose Power Factor and then returned out of the menu.
 
How many watts total is the array?
In 1. Setup>2. Grid STD>1. React Mode>What is your setting?
How many amps are you charging with?

Reason I ask is I have reported the issue with Bus over VOL and Bat over Vol. Been testing and I used Power Factor instead of React Power yesterday. Ran one day smooth as butter. Knock on wood.

As far as charging I had seen similar but only spikes where the charge would quit but picked right back up without any Warnings. I am about 400 watts over paneled on each three arrays. I covered a few cells on each array and seem to help. I also found that with V1.04.09 I can only get about 70 amps before I have drop outs. Before the update I had gone as high as 140 amps without issue. Ran 100-125 for months, again without issues.

Curious to see if we can narrow down some of these issues and understand some of the setting more fully.
Can you elaborate what you mean by using PF instead of reactive power?
 
I see the same morning spikes as everyone else. The unit needs 120v on the DC side to "turn on" the MPPT. It will then hold 85v and allow the current to increase until 1amp. At that point, it allows voltage to increase to find max power of the panels. This has been very consistent.

It does the same in the evening. Once power drops below 100w, it will reduce voltage to 85v and hold there while current tapers to zero.
 
Can you elaborate what you mean by using PF instead of reactive power?
It's my assumption that the four choices are modes? So each is a choice or mode instead of settings that the inverter used from each one. I don't have a clue what QU Wave and QP wave are. In Reactive mode I feel and seem to notice it is the reaction time that the inverter uses to changing loads, especially with anti reverse. When a resistive load turns off I noticed the inverter over shoots and feeds into the grid for a bit. I was worried about this so had Reactive power to +10? I think. But it seemed like the power fed towards grid, and that fed into by grid, jumped around more. Back to PF mode it seems that while it still over shoots, overall the changes look much smoother when looking at external monitor.

Also I noticed that on the external monitor my PF has been more normal. Running in React Mode I would most of the time see .15 +/- on Grid coming in past the CT's. I thought that maybe the inverter does not sync with grid very well. Now it is .35PF @ 60 watts. My PF readings also were a bit wacky on the Grid input of the inverter when feeding towards the grid. Now I show 300 watts @ .90 PF. I even run two Reference transformers to get betting readings on the monitor. They helped with one plugged into the EPS panel and the other into the Main Panel.
 
Here is an example of a few months ago before the two Reference transformers.

Screenshot 2022-03-21 at 06-49-21 IotaWatt.png

Here is a shot of current operation.

Screenshot 2022-07-04 at 09-32-43 IotaWatt.png
 
Hello All, I am looking for a digital copy of the megarevo 8kw owners manual? Any suggestions?
 
This one is the same
 

Attachments

  • GSL 48V Split Phase Hybrid Inverter User's Manual.pdf
    2.3 MB · Views: 34
Does anyone know the firmware version # posted above? I finally got my unit powered up yesterday and the versions that came loaded are:

ARM: V1.03.06
DSP: C1.04.06

I'm told there is 'supposedly' a firmware update coming that will allow parallel of these units, but no idea if that will ever come about.
NCS; I am late to the conversation. I just installed my inverter and having this same problem. Kindly offer a solution if there is one.
 
I was lucky enough to obtain a copy of the latest firmware (Thank you!) and have confirmed that parallel function is now supported for these inverters. Unfortunately, I only have 1 inverter wired up right now since the parallel function was not available when I did the initial install. I'm going to try to get the wiring updated this week, so that I can test out the additional feature and report back.
 
I was lucky enough to obtain a copy of the latest firmware (Thank you!) and have confirmed that parallel function is now supported for these inverters. Unfortunately, I only have 1 inverter wired up right now since the parallel function was not available when I did the initial install. I'm going to try to get the wiring updated this week, so that I can test out the additional feature and report back.
Was there another update since the firmware update from last month?
 