Validation of 12v Battery requirements

Ruburnel

New Member
Joined
Dec 22, 2021
Messages
40
I'm planning to try and power a domestic washing machine from a 12v LiFePO4 battery with a 3Kwh inverter (UK - 230v) and have done some maths but wanted to make sure I'm heading in the right direction.
I've been monitoring the washing machine (running from a normal 230v outlet) over a period of time and have seen it use a maximum of 2200 watts and 1.3Kwh for a complete cycle.
By my calculations (which may well be wrong) I'd need a 200ah battery, due to the fact that the 1300wh / 12v = 108ah, and will also need to be able to pull (2200watts / 12v) = 183amps ?
Please let me know if this is correct....or not.......

Cheers for now

Russell
 
Does your washing machine have a surge associated with the electric motor startup?

Inverter inefficiency factored in to your calculations:

1300Wh/12V/.85 = 127Ah

2200W/12V/.85 = 216A

216A exceed the discharge rating of typical 200Ah cells.
 
Does your washing machine have a surge associated with the electric motor startup?

Inverter inefficiency factored in to your calculations:

1300Wh/12V/.85 = 127Ah

2200W/12V/.85 = 216A

216A exceed the discharge rating of typical 200Ah cells.
Thanks for the response sunshine :)

I assume that the maximum wattage of 2200 was the "surge" but can't be 100% sure tbh as I was just using one of those plug-in digital devices that shows the maximum and minimum wattage and total Kwh since the last reset, etc. From what you've pointed out I might have to have a re-think about using 12v and maybe look at 24v instead.
 
Surge or "inrush" are typically not captured without a specialty tool designed for that feature. Many monitoring devices can capture "max", but that usually isn't the surge.

Can you link a manual for the model of washer? Sometimes the electrical specs give you an idea.

2200W is within the realm of reason for 12V. The ~280Ah cells seem to be the most favorable $/kWh at this point. 24V would required you to purchase 2X, but you could get away with smaller cells and likely keep the cost similar.

Another thing to consider is the BMS. BMS with 100A ratings are prolific. 200A+ are less common.
 
Surge or "inrush" are typically not captured without a specialty tool designed for that feature. Many monitoring devices can capture "max", but that usually isn't the surge.

Can you link a manual for the model of washer? Sometimes the electrical specs give you an idea.

2200W is within the realm of reason for 12V. The ~280Ah cells seem to be the most favorable $/kWh at this point. 24V would required you to purchase 2X, but you could get away with smaller cells and likely keep the cost similar.

Another thing to consider is the BMS. BMS with 100A ratings are prolific. 200A+ are less common.
I've found a UK manufacturer/supplier of 12v batteries that have a 200A discharge rating:


The washing machine is a Hotpoint and I found the attached specification sheet but it doesn't give any idea of the "surge" rating.

Cheers for now
 

Attachments

  • Washing Machine Tech Spec.pdf
    593.9 KB · Views: 4
How long is the wash running for? I have a Hoover washing machine. I have been running it off solar through my AiO. The most I've seen it use was 1.7kwh (heating up the water), thats on a 30C wash for a 59min cycle. My washing machine doesnt use 2kw to do the whole load.

My set up has an electricity monitor in the fuse box, and after 1 wash at 30C on the 59min cycle, it has used about 300watts maybe.

Maybe change your wash cycle so its at a lower temp and a shorter wash ?? Be cheaper on batteries then.
 
I've found a UK manufacturer/supplier of 12v batteries that have a 200A discharge rating:


The washing machine is a Hotpoint and I found the attached specification sheet but it doesn't give any idea of the "surge" rating.

Cheers for now

Based on the datasheet, 13A * 240V = 3,120W

How long is the wash running for? I have a Hoover washing machine. I have been running it off solar through my AiO. The most I've seen it use was 1.7kwh (heating up the water), thats on a 30C wash for a 59min cycle. My washing machine doesnt use 2kw to do the whole load.

My set up has an electricity monitor in the fuse box, and after 1 wash at 30C on the 59min cycle, it has used about 300watts maybe.

Maybe change your wash cycle so its at a lower temp and a shorter wash ?? Be cheaper on batteries then.

Please review your use of kW and kWh.
 
How long is the wash running for? I have a Hoover washing machine. I have been running it off solar through my AiO. The most I've seen it use was 1.7kwh (heating up the water), thats on a 30C wash for a 59min cycle. My washing machine doesnt use 2kw to do the whole load.

My set up has an electricity monitor in the fuse box, and after 1 wash at 30C on the 59min cycle, it has used about 300watts maybe.

Maybe change your wash cycle so its at a lower temp and a shorter wash ?? Be cheaper on batteries then.
Apparently, it's one of those "smart" machines that varies the run time based on the weight of the load and I'm reliably informed by the lady wife that using a 30deg wash is worse than useless in most cases, so I just go along with what she tells me :) It's just a little project for me to play around with while I wait for some 48v LiFePO4 batteries to arrive in stock for the "real" off-grid utility room plan.
If I can't run the washing machine, I can look at the dishwasher instead as we tend to run that on the "economy" setting which will hopefully be less power hungry than the WM :unsure:
 
Based on the datasheet, 13A * 240V = 3,120W



Please review your use of kW and kWh.
Most UK appliances have a 13A fuse/rating but I've just noticed the line above the Current says "Electrical connection rating (W) = 1850, so maybe the 2200W I've seen includes the "surge"?
 
I think we can say that my original calculations were pretty accurate, apart from missing the 85% efficiency of the inverter (y)

Having said that, I could use a voltage of 12.8 as that seems to be the nominal voltage of the 12v battery that I've been looking at:

1300Wh/12.8V/.85 = 119Ah

2200W/12.8V/.85 = 202A
 
I'm planning to try and power a domestic washing machine from a 12v LiFePO4 battery with a 3Kwh inverter (UK - 230v) and have done some maths but wanted to make sure I'm heading in the right direction.
I've been monitoring the washing machine (running from a normal 230v outlet) over a period of time and have seen it use a maximum of 2200 watts and 1.3Kwh for a complete cycle.
By my calculations (which may well be wrong) I'd need a 200ah battery, due to the fact that the 1300wh / 12v = 108ah, and will also need to be able to pull (2200watts / 12v) = 183amps ?
Please let me know if this is correct....or not.......

Cheers for now

Russell
First question - what is your inverter's Pf (power factor)?

Second question - is your inverter a 12V or 24V unit?
 
I should have updated this thread a while ago, as I purchased a Roamer 160ah 12v battery and it has been happily running our Washing Machine via a 3000W 12 v Inverter from FCHAO :)
 